If I recall, I believe Sch 7 pipe became popular for use in Press-Fit 
systems. And I think that was galvanized, nit black. Outside of that I haven’t 
seen a situation where it gives you any significant advantage over sch 10. 
However, if it is listed for fire service, it is would be acceptable.
  

  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Jan 8, 2024 at 12:14 PM,  <Ryan Hinson (mailto:[email protected])>  
> wrote:
>   
>   
>           
>   
>
> If it is listed for FP use and appropriate for the pressure classification 
> needed for your system, then yes.    See below for additional relevant NFPA 
> 13 (2022) requirements and considerations:
>
>   
>
>   
>
>   
>
> 7.3 Aboveground Pipe and Tube.
>
>   
>
> 7.3.1 General.
>
>   
>
> 7 .3.1.1   Pipe or tube shall meet or exceed one of the standards in Table 
> 7.3.1.1 or be in accordance with 7.3.3.
>
>   
>
>   
>
>   
>
> 7.3.3* Listed Metallic Pipe and Tubing.
>
>   
>
> 7.3.3.1   Other types of pipe or tube investigated for suitability in 
> automatic sprinkler installations and listed for this service, including 
> steel, and differing from that provided in Table 7.3.1.1 shall be permitted 
> where installed in accordance with their listing limitations, including 
> installation instructions.
>
>   
>
>   
>
>   
>
> A.7.3.3   Other types of pipe and tube that have been investigated and listed 
> for sprinkler applications include lightweight
>
>   
>
> steel pipe. While these products can offer advantages, such as ease of 
> handling and installation, cost effectiveness, and reduction of friction 
> losses, it is important to recognize that they also have limitations that are 
> to be considered by those contemplating their use or acceptance.
>
>   
>
> Corrosion studies have shown that, in comparison to Schedule 40 pipe, the 
> effective life of lightweight steel pipe can be
>
>   
>
> reduced, the level of reduction being related to its wall thickness.    
> Further information with respect to corrosion resistance is contained in the 
> individual listings for such pipe.
>
>   
>
>   
>
>   
>
> The references in Table 7.3.1.1 will provide information on whether the pipe 
> wall thickness you want to use, is listed per that reference.
>
>   
>
>   
>
>   
>
> 16.3.2* Steel Pipe - Welded or Roll-Grooved. When steel pipe referenced in 
> Table 7.3.1.1 is used and joined by welding as referenced in 7.5.2 or by 
> roll-grooved pipe and fittings as referenced in 7.5.3, the minimum nominal 
> wall thickness for pressures up to 300 psi (21 bar) shall be in accordance 
> with Schedule 10 for pipe sizes up to 5 in. (125 mm), 0.134 in. (3.4 mm) for 
> 6 in. (150 mm) pipe, 0.188 in. (4.8 mm) for 8 in. and 10 in. (200 mm and 250 
> mm) pipe, and 0.330 in. (8.4 mm) for 12 in. (300 mm) pipe.
>
>   
>
>   
>
>   
>
> See Table A.16.3.2 for steel pipe dimensions including pipe wall thicknesses 
> down to Schedule 5.
>
>   
>
>   
>
>   
>
> Allowable piping this thin has connection-type restrictions:
>
>   
>
>   
>
>   
>
> 16.3.3 Steel Pipe – Threaded. When steel pipe referenced in Table 7.3.1.1 is 
> joined by threaded fittings referenced in 7.5.1 or by fittings used with pipe 
> having cut grooves, the minimum wall thickness shall be in accordance with 
> Schedule 30 pipe [in sizes 8 in. (200 mm) and larger] or Schedule 40 pipe [in 
> sizes less than 8 in. (200 mm)] for pressures up to 300 psi (21 bar).
>
>   
>
> 16.3.4 Specially Listed Steel Pipe. Pressure limitations and wall thickness 
> for steel pipe specially listed in accordance with 7.3.3 shall be permitted 
> to be in accordance with the pipe listing requirements.
>
>   
>
>   
>
>   
>
> Piping less than Sch. 10 does not have the same bending requirements for fire 
> protection per NFPA 13 Section 16.3.8 below:
>   
>   
>
>   
>
> 16.3.8 Metallic Pipe and Tube Bending.
>
>   
>
> 16.3.8.1   Bending of Schedule 10 steel pipe, or any steel pipe of wall 
> thickness equal to or greater than Schedule 10 and Types Kand L copper tube, 
> shall be permitted when bends are made with no kinks, ripples, distortions, 
> or reductions in diameter or any noticeable deviations from round.
>
>   
>
> 16.3.8.2   For Schedule 40 and copper tubing, the minimum radius of a bend 
> shall be six pipe diameters for pipe sizes 2 in. (50 mm) and smaller and five 
> pipe diameters for pipe sizes 2½ in. (65 mm) and larger.
>
>   
>
> 16.3.8.3   For all other steel pipe, the minimum radius of a bend shall be 12 
> pipe diameters for all sizes.
>
>   
>
> 16.3.8.4   Bending of listed pipe and tubing shall be permitted as allowed by 
> the listing.
>
>   
>
>   
>
>   
>
> Hope this helps,
>
>   
>
>   
>
>   
>   
>
>  Ryan L. Hinson, PE*, SET**    \    Burns  &  McDonnell
>
>   
>
>  Associate Fire Protection Engineer \ Upper Midwest Region
>
>   
>
>  O    612-900-3755\      M    763-688-4045 \      F    952-229-2923
>
>   
>
>  [email protected] (mailto:[email protected])    \      burnsmcd.com 
> (http://www.burnsmcd.com/)
>
>   
>
>  8201 Norman Center Drive, Suite 500    \    Bloomington, MN 55437
>
>   
>
>  *Registered in: AK, LA, MD, MN, PA, TX,  &  UT
>
>   
>
>  **NICET IV - Water-Based Systems Layout
>
>   
>   
>
>   
>
>   
>   
>   
>
> From:   Luis Perea  <[email protected]>
>   Sent:  Monday, January 8, 2024 10:28 AM
>   To:  [email protected]
>   Subject:  [Sprinklerforum] LIGHT-WALL SCH 7 NFPA
>
>   
>   
>   
>
>   
>
>   
>
> Hi Everyone,
>
>   
>
>   
>
>   
>
> According to NFPA is it permitted to use light-wall sch 7 for branclines? Or 
> sch 10 is a must?
>
>   
>
>   
>
>   
>
> Thanks,
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>
>
>   
>
>   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to