Tom,
  

  
You are right on target. The spray booth is for painting auto body parts. I 
have done a few of these recently, but in this case, the people I have been 
dealing with are about as sharp as a bowling ball. I’m not sure they know how 
it works. I will be finding out more in the next couple of weeks.   
  

  
I am doing sprinklers only on this. The design will be Extra 2. There are 
enough challenges there. Any monitoring and maintenance is beyond my agreement. 
However, they were talking about putting the intake and exhaust ducts side by 
side through the roof. I may have to get involved in that one.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Dec 26, 2023 at 4:56 PM,  <Thomas Reinhardt 
> (mailto:[email protected])>  wrote:
>   
>   
>         
>   
>
> Todd,
>
>   
>
> As you probably know check what codes are adopted.
>
>   
>
> 1.Find out exactly what they will be spraying. SDS.
>
>   
>
> 2. IFC chapter 24
>
>   
>
> 3. NFPA 33
>
>   
>
> 4. Sounds like you have a down draft spray booth. Intake from the ceiling 
> then out the floor vents then discharged up and out.
>
>   
>
> 5.Intake and exhaust are required.
>
>   
>
> 6. Only the exhaust duct needs to be protected.
>
>   
>
> 7. Air monitoring is required.
>
>   
>
> 8. All filters need to be changed regularly and disposed properly.
>
>   
>
> 9. Numerous other requirements.
>
>   
>   
>   
>
> From:  Fpdcdesign  <[email protected]>
>   Sent:  Tuesday, December 26, 2023 1:52 PM
>   To:  Sprinklerforum  <[email protected]>
>   Subject:  [Sprinklerforum] Sprinkler is spray both intake ducts.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>   
>   
>   
>   
>   
>
>   Caution:   This is an external email, Please take care when clicking links 
> or opening attachments. When in doubt, please talk with the sender or check 
> with VOP IT
>
>   
>   
>   
>   
>   
>   
>
>   
>
>   
>   
>   
>
> I am working on a project where a company acquired a   used paint spray booth 
> that they are adapting to their operation. It is a little unique in that the 
> air intake is through the floor and the exhaust is through the ceiling. The 
> previous dry chemical system has been removed and the booth is now to be 
> protected by sprinklers. Sprinklers for the booth area, control room and 
> exhaust ducts are a given. However, the intake air goes from the ductwork to 
> a plenum below the floor. Between the plenum and the spray area is a set of 
> filters. I have no idea if they are combustible or not and neither does 
> anyone else. Normally I would not give much consideration to protecting the 
> intake air system, but these filters may be an issue. Has anyone run into 
> this type of booth and what have they done about the intake?   
>
>   
>   
>
>   
>
>   
>   
>   
>
> Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to