Thank you, Brett, I appreciate all of the information.

I hope you have a Merry Christmas and Safe and Happy New Year

Charlie


From: Brett Peters <[email protected]>
Sent: Friday, December 22, 2023 11:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Painted Heads

This message originated from outside the Ithaca College email system.

If you can find a sprinkler with the same k factor and spray characteristics 
then you can just replace it.
There is also a provision in the code book that says if the exact sprinkler is 
not available you can replace it with a sprinkler that is similar in k factor 
and spray pattern.
NFPA 25

5.4.1.3* Special and quick-response sprinklers as defined by NFPA 13, Standard 
for the
Installation of Sprinkler Systems, shall be replaced with sprinklers of the 
same orifice, size,
temperature range and thermal response characteristics, and K-factor.

A.5.4.1.3 It is imperative that any replacement sprinkler have the same 
characteristics as the
sprinkler being replaced. If the same temperature range, response 
characteristics, spacing
requirements, flow rates, and K-factors cannot be obtained, a sprinkler with 
similar characteristics
should be used, and the system should be evaluated to verify the sprinkler is 
appropriate
for the intended use. With regard to response characteristics, matching 
identical Response
Time Index (RTI) and conductivity factors is not necessary unless special 
design considerations
are given for those specific values.


Proudline will be closed over Christmas from Saturday December 23 to Tuesday 
January 2.

Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]<mailto:[email protected]>
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca<http://www.proudline.ca/>

Proudline now offers ULc listed monitoring services, please contact 
[email protected]<mailto:[email protected]> for more information



[https://ci3.googleusercontent.com/mail-sig/AIorK4wRo6r0eNDUWx8YR-4XJLvwcnouQn_xEZH_HIb4jDbepWtON2RWC-ekzvZHKtncFOQqPcNQfzM]
 
[https://ci3.googleusercontent.com/mail-sig/AIorK4yJVI287VPLDWiW9maE2Np3U4CdszCY9deeyaLl8DM90wlBd7pnuOZV9U-swv-7gWN_24py6vo]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4wlGmqj6Ja06DKOIMLPvEE8B2W8fT_TPPA3w-4JfqygLq9n77ECSni09YLIVICXJYzWo4Z0PjU]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4zEgPbs279KVEfWIpIiWNLel8zAlcloW9dNXGLTaE1cMz88CRkmg17fju5BQB_iIzhWK20DUL8]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4z7J0kfmSGA8jKvDK0pTqW3KQlc5v-tYcWosmy5W7pdok462Gzu_9Ft7UK9oJUWDT1DzhQ4hUU]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4wTVHoTZxkppBoWSCTFnGLgGTq0apivi8sNvWPyBsloO0mmy8ZYu4Ax854jo7ihTMFyeYeOceg]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4xwBWEOX5v9mpza4Jqf9lOKSwThBNvyIO7Rl-Cxo7NRiV7p70C0f1biwbh44Y-iIA5GcmD1MCo]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4yPfO1HdtbQPYiKlYE38cwc88ABhX7xN1nh0fCK5LjFXjKplJggk3Xn6_XypmtMWyADKR7ZRGk]


On Fri, Dec 22, 2023 at 9:39 AM Charlie Sherman 
<[email protected]<mailto:[email protected]>> wrote:
Hello,
We were cited for a sprinkler that has been painted, and unfortunately is no 
longer in production.  Residential townhouse type occupancy, college students.

Is it necessary to replace all heads in the apartment, or can it be just the 
affected head?  I have opposing opinions and am looking for some assistance.  
Is there any code or standard that references this issue?

Thank you!
Charlie


Charlie Sherman
Fire and Building Safety Coordinator
Ithaca College Office of Public Safety & Emergency Management
953 Danby Road
Ithaca, New York 14850
607-274-3333
[email protected]<mailto:[email protected]>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to