If you’re in the 2018 IFC, look at Section 5106. It has the requirements.
From: George Medina Jr. <[email protected]> Sent: Thursday, December 14, 2023 5:11 PM To: Discussion List On Issues Relating To Automatic Fire Sprinklers <[email protected]> Subject: [Sprinklerforum] Retail Sales of Aerosols Level 2 You don't often get email from [email protected]<mailto:[email protected]>. Learn why this is important<https://aka.ms/LearnAboutSenderIdentification> ⚠ CAUTION: External Email I have a smoke shop retail store where the fire inspector flagged them to apply for a hazardous material fire permit for the sales/storage of 2,730 11 ounce cans of level 2 aerosols (Spray Paint). I looked in NFPA-30B (It addresses only rack, palletized or solid piled storage) of high roof facilities. I also looked at NFPA-13 and only found Level 1 aerosol classifications (III). I have a retail store with a ceiling height of 10' with a display about 7 feet high with about 6 rows of aerosols. Could I classify it as a regular Ordinary Hazard Group 2? (Retail) or Can anyone direct me to the correct code section? Thanks George Medina Jr. Sr. Fire Sprinkler Designer SINGLETON FIRE PROTECTION INC. Cell: (323) 906-5701 Business Hours: 9:00am-5:00pm
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]