Tim

                The equipment shouldn't be an issue if  only service people
are accessing the space.  The issue is those old  buildings have walk up
stairs and floors which someone will find it is a great space for storage.
If a stepladder is needed to get into the attic you may be ok.  

From: [email protected] <[email protected]> 
Sent: Monday, December 11, 2023 12:08 PM
To: [email protected]
Subject: [Sprinklerforum] Definitions

 

I am working on a unheated Attic of 6800 SF wood framing with a Ridge Pole
29' above the upper floor ceiling structure. The structure was built in
1893.

The Building is being renovated which includes new HVAC with air handling
equipment to be installed in the Attic. No heating equipment. The attic will
not be used for Storage.

 

Will the presence of Air Handling equipment negate the definition of an
"unused Attic"? Does the presence of any HVAC equipment put the occupancy
into Ordinary Hazard?

 

If there is a definition in NFPA FOR "Unused Attic", I am unable to find it.

 

 

Regards,

G. Tim Stone

 