The letter and intent of the standard is to calculate 500 GPM from the 2 most 
demanding hose connections on the hydraulically remote standpipe, then add 250 
GPM at the connection point to the feed main serving the additional standpipes, 
up to the required maximum flow rate for the building.   If the remote 
standpipe has a 2-way roof header, we take it there (also, it's a practice 
that's enforced by just about every AHJ in California).   If  you have only one 
hose connection at the top of the remote SP, then take 250 at that one and 250 
from the next-most remote one and run your 500 back to the feed main that way.

I hope this answers your question, otherwise I'm not understanding it clearly.

The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Protection Design and Consulting
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training







From: Brian Harris <[email protected]>
Sent: Wednesday, November 29, 2023 1:06 PM
To: [email protected]
Subject: [Sprinklerforum] 2 Most Remote Hose Valves For Standpipe Calc

At one point calculating a standpipe meant having (2) hose valves on the same 
floor and then calculating (1) each on the other standpipes as needed. Is the 
current train of thought adding the "extra" valve on the most remote standpipe 
not required and just catching one on the floor below good enough?

Thank you,

Brian Harris, CET
BVS Systems Inc.