Tim

                Check FPA1  I believe I it does but only required control
valves for each level so the whole building does not have to be shut down.
Buildings up to 4 stories can be considered one zone for the sprinkler
system.  Each floor should be zoned through the detection system. 

                Terry in So. Burlington also has it in their ordinances. 

dick

 

From: [email protected] <[email protected]> 
Sent: Thursday, November 09, 2023 8:53 AM
To: [email protected]
Subject: [Sprinklerforum] Floor Zone Control Assemblies

 

Floor Zone Control Assemblies in Multistory buildings exceeding 2 stories in
height are required in accordance with NFPA 13.

 

Is this also required in residential buildings designed in accordance with
NFPA 13R? The building in question is 3 stories and of wood frame
construction.

 

Regards,

G. Tim Stone

 