I can’t come up with any great exceptions for the soffit scenario, but 
personally I’d either try and get them to gyp board over the wood above and if 
needed board it off every 160 cubic feet to make it meet 9.2.1.11 or stuff it 
with non-combustible insulation.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: Fpdcdesign <[email protected]>
Sent: Wednesday, October 4, 2023 10:54 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Irregular concealed space sprinkler spacing

I am working on a project in a wood frame building where they have ceilings at 
varying heights. In the high ceiling areas (about 50% of the space), there is 
5” between the ceiling and the bottom of the joists. These do not require 
sprinklers
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message originated outside your organization.
ZjQcmQRYFpfptBannerEnd
I am working on a project in a wood frame building where they have ceilings at 
varying heights. In the high ceiling areas (about 50% of the space), there is 
5” between the ceiling and the bottom of the joists. These do not require 
sprinklers per 
9.1.2.5<https://urldefense.com/v3/__http:/9.1.2.5__;!!FaxH778!cYzBdsgz8AObkbOYmm-JRNJkKPR9TrVEZ9baALwDLcuDTJbGuVCzJgLKR4CpxZkUI3Vy2oTEqpDONN8rZDA$>.
 In the low ceiling areas, there is 10” to 12”, so concealed space sprinklers 
would need to be installed above those. There are also soffits along some walls 
that are 18” to 24” wide that technically would require sprinklers even though 
the surrounding areas don’t. Is there a point where I don’t need consider small 
spaces in placing CC’s?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to