Steve-
There’s clearance above each deflector to the insulation. AHJ said he wants min 
4”.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Steven Jenkins <[email protected]>
Sent: Friday, September 29, 2023 9:51 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Spray Foam Insulation

I wonder if the original direction was to the foam insulation installer.
Something along the lines of, “Don’t spray the foam closer than 4” to a 
sprinkler.”
For foam that expands, I can easily see where foam that was sprayed closer than 
4” would cover the sprinkler before it cured.

M2C

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Friday, September 29, 2023 7:46 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Spray Foam Insulation

---- SCDLLR NOTICE (M365) ----
•  This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
•  Personally Identifiable Information (PII) should not be included in e-mail 
text or attachments. Do not save or transmit PII unencrypted.
Agreed. Sure sounds easier for them to shave the insulation to a consistent 
depth instead of cutting back sprigs.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,k99W6WC88YSP68n2n-aRrHpoX17bbkam06vE-zcyGNMsfEqOU4GZE5DQaHH1lh9480FLVKeEfIib5icDXDBpKvKToxtFUrvFNFHmBi2t-qykY_3DW6EaSQ,,&typo=1>


From: [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Sent: Friday, September 29, 2023 7:15 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Re: Spray Foam Insulation

Sounds like the AHJ needs to be talking to the spray foam folks.

Too often we take on problems that are clearly not ours.


R/
Matt

Please rate our customer 
service<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fsurvey.medallia.com%2f%3femailsignature%26fc%3d3539%26bg%3dFire%2520and%2520Fabrication&c=E,1,XPjMFgVNniW3HSqOKW2EgiwHZFWhB8QvoSwJgAJMExy_8ZlY0E8__-_VmCXjI-_P0oPQ5eiP-xa_8_XEN2LqIFAiaM0oJU280IHeJQK8zlmM&typo=1>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
3508 Hwy. 557
West Monroe, LA. 71292
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.fergusonfire.com%2f&c=E,1,KyFqvFe26Wyy531nc4ze3_TjjYjFbWJvznGSRx5sBjx86SAsV3T2_YNiD7WBbLuHdwUCx5RC9tXWo4eTltNV7DNkYetyU4qxh7DOZrr9&typo=1>


From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Friday, September 29, 2023 7:09 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Spray Foam Insulation

One of the problem is that insulation installers are not consistent. Some may 
stop at the joists, others may just let it flow. It is almost impossible to 
properly install sprinks until after the insulation is in, but then it is 
difficult to hang the pipe.

On one job I was working on, the insulation contractor buried a line of attic 
sprinklers.


On Sep 29, 2023 at 6:46 AM, <Brian Harris<mailto:[email protected]>> 
wrote:
Craig-
No, this is spray on insulation in an attic.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,49Sr2tnJsfAbzwzuZfq5yuEWqf7oJl7cCmNasyTI2mRYBGtkdqMShPzkFC6t7YJP7mFhkTPxYkeEEi0_6hGhEQYz7etu5gzQVp7MkteHs5Fnj2tu&typo=1>


From: Craig Hanson <[email protected]<mailto:[email protected]>>
Sent: Thursday, September 28, 2023 6:07 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Spray Foam Insulation

Are they referring to the exposed barrel length for dry heads in freezers?



Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
C: 253.225.9977 | E: [email protected]<mailto:[email protected]> | 
www.WC-3.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.wc-3.com%2f&c=E,1,G-qJtnVYuPtBsagbJiEVzFJ0WEU5CYTDyuK47610o1m6P5LSztgC6fmrJKM3imJRppfCEW0khFMJLZnuLUgg9yJROPJY3yDpcV87eCTzHEHqaeo,&typo=1>
Teaming With Your Community to Make a Difference


On Thu, Sep 28, 2023 at 3:56 PM Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Ken-
Thanks and will do.
Sent from my iPhone

On Sep 28, 2023, at 5:31 PM, Ken Wagoner 
<[email protected]<mailto:[email protected]>> wrote:
 And I will be very interested to find what "code" they're referring to.

I submit that if one is to consider the spray foam insulation as unobstructed 
as defined by -13, then the deflector position relative to the bottom level of 
the foam is required to be between 1" and 12" per 10.2.6.1.1 ('22 edition).

If the bottom of the insulation is to be considered as obstructed, or the foam 
is between members which are obstructed, then the deflector must be 1" to 6" 
below the member, but no greater than 22" down from the ceiling/roof deck 
above, per 10.2.6.1.2 ('22 again).

I can't wait to learn the rationale behind such a requirement.

In short, remember my oft repeated mantra, whenever someone pops up with 
something like this:  Prove it.

keep the forum informed, ok?
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
On 9/28/2023 2:12 PM, Brian Harris wrote:
The AHJ is supposed to be providing the “code” where this came from. Should be 
interesting.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,NvV0ykxyRIDiQmNmnF1YVfzIf9e-XjJf0jAYRH-j5x-Jl4h0VEdXiDYM2z3SzR3x1AtaqZPNcNqSxscq3s9bN1qiWiCOi3VwENv7mxFR-A,,&typo=1>


From: Eric Rieve <[email protected]><mailto:[email protected]>
Sent: Thursday, September 28, 2023 2:54 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]><mailto:[email protected]>
Subject: [Sprinklerforum] Re: Spray Foam Insulation

Funny enough I was told the same a few years ago. His reasoning was that the 
uneven nature of the foam application could cause obstructions that weren’t 
readily apparent so extra clearance was warranted.

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Thursday, September 28, 2023 2:48 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Spray Foam Insulation

Anybody ever have an AHJ say you need 4” clearance from the bottom of spray 
insulation to the deflector?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,wo5wYVtpGosaBntgPq_5rudqm8ADj3XpDv10H3ACDcs2pNvWgifdhkbEDh5cNdO54rGdJmuywOvI-uxu4wi0CjpghGrXuaIGLLlPSAjRPh_ujRUBa-eEnA,,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935




_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,d6tW2jgARtGVB02AxLLmHdgE0tA40fBzchQKqyzszMTLIwhOtF-rDC7Vx7qpysDQ2KRsXHURW0q7fbhEe9E2JSkM7dj4IaBrBwk5xtYFKHtNj3bzrLs9G74,&typo=1>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,Htkmtxh_o8Eb5uL84eDw_HCeUpb2y_GQV1V9WyygyEVlGFLr9hMw9_5fbGsLvjn3feWQDEZ8CaDkDx2kHVsPT9WQed6T8poTKciobc3yOdTT&typo=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,BDhc_XksCTtpzYOibdzPF-1SNzjdI88u_vkqtK38JlQcBxZkFOyz2vDY43vUq4dlTIlazAcA1VcHkN_Y3IAozH0npUd2EolVg9aiUKTVOs-Two6A_fz3zC8,&typo=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,g-QaP78twj9UKTXMSa7j4cmP-5E9kaTz47VIZhSuL_hpdRl-0fOiATRJq55PwVbYneD7HOTmnCQLcX6tNfAKaScO-XDy0A6ibPJ_KoTxL64V8mbN&typo=1>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to