I don't believe it states whether the spacing is along branches or between Max spacing is 12'-0 but max coverage is still only 100sqft
Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection Services Ltd. [email protected] 780 490 7602 office ext 202 780 490 7605 fax 780 777 0568 cell 780 718 2676 24h Visit us at www.proudline.ca Proudline now offers ULc listed monitoring services, please contact [email protected] for more information On Mon, Sep 25, 2023 at 1:40 PM Joe Burtell [MT-BILL] < [email protected]> wrote: > Is the spacing of 12’ in building less than 30’ in table 14.2.8.2.1 of the > 2019 NFPA 13 along the branchline or can it be between the branchlines? I > feel it’s along the branchline but can’t find my confirmation. > Joe > > Burtell | SET, CFPS > Fire Sprinkler Manager > D > C > > > 406-204-4653 > 406-861-4507 > 3004 1st Ave South > Billings > , > MT > 59101 > Office: > 406‑652‑7697 > www.summitfiresecurity.com > This information transmitted, including attachments, is intended only for > the person(s) or entity to which it is addressed and may contain > confidential and/or privileged material. Any review, retransmission, > dissemination or other use of, or taking of any action in reliance upon > this information by persons or entities other than the intended recipient > is prohibited. If you received this in error, please contact the sender and > destroy any copies of this information. > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected] >
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]
