I have consecutive beams I must penetrate with a 4" main through a 5" hole in the steel beam. I do not have clearance, so I have provided flexible couplings on both sides of the beam. First question is do I need to provide clearance; they are consecutive holes? Next question, is if I do need clearance and I use flex couplings because I don't have the clearance necessary, do I have to add additional lateral bracing because of the flexible couplings? The hole is not used to support the pipe, there will be hangers to the tops of the steel I-beams.
2019 NFPA 13 Joe Burtell | SET, CFPS Fire Sprinkler Manager D C 406-204-4653 406-861-4507 3004 1st Ave South Billings, MT 59101 Office: 406-652-7697 www.summitfiresecurity.com This information transmitted, including attachments, is intended only for the person(s) or entity to which it is addressed and may contain confidential and/or privileged material. Any review, retransmission, dissemination or other use of, or taking of any action in reliance upon this information by persons or entities other than the intended recipient is prohibited. If you received this in error, please contact the sender and destroy any copies of this information.