I think, a dangerous thing, and based totally on speculation, without any
supporting information, the grv x flg could be used due to vibration. I can
visualize something as heavy and lopsided as an OS&Y rotating. Again, just
pure speculation.

On Tue, Sep 12, 2023 at 6:31 AM Brian Harris <[email protected]>
wrote:

> Thank you.
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
>
>
>
>
> *From:* Taylor Schumacher <[email protected]>
> *Sent:* Tuesday, September 12, 2023 9:10 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: Pump Suction Components
>
>
>
> I don’t know of a requirement for flanged fittings in the suction side.
> OS&Y valves typically came FxF and hence the suction side fittings would
> all be flanged. Grooved OS&Y is becoming more popular… That being said, I
> have yet to see a pump with grooved inlets and outlets.
>
>
>
> Pros to all grooved are they are quicker to install.
>
> Pros to all flanged is they create a more stable/sturdy connection.
>
>
>
>
>
> *Taylor Schumacher*
>
> Security Fire Sprinkler
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.j-berd.com%2f&c=E,1,IdlECah-jJsrUITlM1aHPd6_WK9pcRGWuxRsi4zNc392EG0I7XP-24ePThtb0cI7OVoYGiTRgfgIrNkG1f9GlRSHwMaBLCv8gV5H6BJ4BgCRXoaZ5c5hQIo,&typo=1>
>
> 1 Industrial Blvd | Sauk Rapids, MN 56379
>
> Office: 320.656.0847 | Direct: 320.640.7050
>
>
>
> *From:* Brian Harris <[email protected]>
> *Sent:* Tuesday, September 12, 2023 7:48 AM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] Pump Suction Components
>
>
>
> *Caution:* This email originated from outside your organization. Please
> take care when clicking links or opening attachments.
>
>
>
> I’ve seen two schools of thought with regard to pump suction components.
> One way is flanged on the suction side and grooved on the discharge. The
> other is all grooved. I can; t see where NFPA-20 requires it either way.
> What’s the popular choice and are there pro’s & cons?
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssystemsinc.com
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,MfgrlWBYwY3PlDOWHES1uoDPWHIDLyk880pEmjCFRCQxPzYOC96WZrZ4GDIi0NbLt1yvzTfJOj1UUcDKHivbv2RBb37AZLuWdTm3Z_pLqkkxBxz7gc8K&typo=1>
>
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to