Look into the QRS system from Tyco, it’s an electronic quick opening device. we 
have used this system on some very large dry systems and it worked very well.
Each panel can control up to four dry systems so you’ll need three panels.

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>



From: Lamar Vaughn <[email protected]>
Sent: Tuesday, August 29, 2023 9:54 AM
To: Sprinkler FORUM <[email protected]>
Subject: [Sprinklerforum] Very Large Dry pipe Systems

Hello All,

I have encountered a building with at least 12 dry pipe systems. These systems 
were installed around 1995 as combined dry pipe/preaction systems.Using a pilot 
line detection method to make it combined systems, to avoid the 1 minute trip 
time requirement for the systems. The pilot lines have since been disconnected, 
leaving them now as just dry pipe. The capacity of most of the systems is about 
1,700 gallons with a trip time of 4 minutes or so.

I don't believe an accelerator will help very much with these. My question is 
this, is there a large exhauster suitable for use on the ends of the systems to 
help with the discharge of air to get these trip times down?

Thanks in advance for any help.

Respectfully submitted,

Lamar Vaughn
Vaughn & Company
678-429-3563

[https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fs-install.avcdn.net%2fipm%2fpreview%2ficons%2ficon-envelope-tick-green-avg-v1.png&c=E,1,METO_lt9OaW8PHUj95axojql91tfFzy02b-a4QXMFeZwgwSX2wOx_Q_vo5Sn0CEP-l8ysleG4sr7TFvQ3VkNY3N0EoKoFUMsuzXjRPFjMzNr9xuW_wT13d4,&typo=1]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>
Virus-free.www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to