Re: “tying into the roof drain in the same stairwell” -   Roof drains are not 
allowed within exit enclosures.  

 

Re: NFPA 101: 7.1.3.2.1(10) (2018 edition) -

Penetrations into, and openings through, an exit enclosure assembly shall be 
limited to the following:

(a) Door assemblies permitted by 7.1.3.2.1(9)

(b) Electrical conduit serving the exit enclosure

(c) Required exit door openings

(d) Ductwork and equipment necessary for independent stair pressurization

(e) Water or steam piping necessary for the heating or cooling of the exit 
enclosure

(f)  Sprinkler piping

(g) Standpipes

(h) Existing penetrations protected in accordance with 8.3.5

(i) Penetrations for fire alarm circuits, where the circuits are installed in 
metal conduit and the penetrations are protected in accordance with 8.3.5

 

Re: IBC (2018) 1023.5 Penetrations. 

Penetrations into or through interior exit stairways and ramps are prohibited 
except for the following:

1. Equipment and ductwork necessary for independent ventilation or 
pressurization.

2. Fire protection systems.

3. Security systems.

4. Two-way communication systems.

5. Electrical raceway for fire department communication systems.

6. Electrical raceway serving the interior exit stairway and ramp and 
terminating at a steel box not exceeding 16 square inches

 

 

 

 

David L. Miller, P.E.

Engineered Fire Protection, LLC

11920 Richcroft Avenue

Baton Rouge, Louisiana  70814

225-273-5040

 

From: Brian Harris <[email protected]> 
Sent: Wednesday, August 23, 2023 12:03 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Roof Drain / Sprinkler Drain

 

Steve-

Very much appreciated.

 

Brian Harris, CET

BVS Systems Inc.

bvssytemsinc.com <http://bvssystemsinc.com/> 

 

 

From: Steve Leyton <[email protected]> 
Sent: Wednesday, August 23, 2023 12:14 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Roof Drain / Sprinkler Drain

 

Not so fast everyone. 

 

The answer to this question depends entirely on your location and the 
state/local rules that may apply to managing storm water runoff and what is 
allowed to enter the watershed via the storm drain system.   It’s easy poke fun 
at CA because of our sometimes-suffocating regulatory environment, but it is 
now illegal to direct sprinkler water into the storm system.  In fact, in most 
incorporated cities and counties, you cannot dump onto hardscape if water could 
run to the storm system.  And CA is NOT the only state in the West with such 
restrictions – anywhere that water can run into the ocean, a bay or lake or 
river, we are now seeing these restrictions.

 

Personally, I understand that if sprinkler water can enter a watershed, it will 
contaminate it and I accept these regulations as a necessary pain-in-the-ass.   
 The challenge is not how to resolve new builds, it’s to deal with 
T.I./expansion projects and ITM throughout the built environment where old 
school test/drain discharge is open to the public way.   There are bio filters 
(sand/oil) for the storm system that may be acceptable to enable discharge, but 
the project civil or owner has to get the private storm system approved if 
using that approach and water cannot enter the public system.  Civil engineers 
and landscape architects engage bio-swales and detention features, and we 
sometimes coordinate with various means to get discharge to percolate into 
softscapes on site.   

 

But the best and most basic approach is to coordinate with the plumbing 
engineer and arrange for a hub drain (4” self-priming trap, 4”-->6” concentric 
increaser to a rubber-booted hub) to be roughed into the riser room.   This 
enables adequate capacity for main drain and inspector’s tests, vents the drain 
per code and controls stinky smells.   In your basement application, we would 
assume that there’s a sewer sump with an ejector, so take it to a hub drain in 
the basement or directly to the sump if you can.   If you’re draining through a 
hose valve, you can obviously drop a hose to the sump.   If one’s not being 
provided, ask for it and point out the challenge of ITM to ownership if the 
building’s not so equipped. 

 

My 4¢,

Steve L.   

 

From: Brian Harris <[email protected] 
<mailto:[email protected]> > 
Sent: Wednesday, August 23, 2023 6:43 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected] 
<mailto:[email protected]> >
Subject: [Sprinklerforum] Re: Roof Drain / Sprinkler Drain

 

Skyler-

Thank you, will do.

 

Brian Harris, CET

BVS Systems Inc.

bvssytemsinc.com <http://bvssystemsinc.com/> 

 

 

From: Skyler Bilbo <[email protected] <mailto:[email protected]> 
> 
Sent: Wednesday, August 23, 2023 9:32 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected] 
<mailto:[email protected]> >
Subject: [Sprinklerforum] Re: Roof Drain / Sprinkler Drain

 

In most cases/places, the sprinkler water is considered gray water, and it 
would be OK to discharge a sprinkler drain to a storm sewer (this is most 
likely where it would end up if you have ever piped a sprinkler drain out an 
exterior wall). This is not OK everywhere, so for your specific project, it 
would be best to ask the AHJ and the plumber (and possibly the plumbing 
inspector) on the project if it is OK. 

 

-Skyler

 

On Wed, Aug 23, 2023, 8:25 AM Brett Peters <[email protected] 
<mailto:[email protected]> > wrote:

I think that would depend on the municipality, most do not want the sprinkler 
water going directly into the storm drains, drained to exterior or into a waste 
drain


 

 

Thanks

 

Brett Peters

General Manager Installation & Design

Proudline Fire Protection Services Ltd.

[email protected] <mailto:[email protected]> 

780 490 7602 office ext 202

780 490 7605 fax

780 777 0568 cell

780 718 2676 24h

Visit us at www.proudline.ca <http://www.proudline.ca/> 

 

Proudline now offers ULc listed monitoring services, please contact 
[email protected] <mailto:[email protected]>  for more information

 

 

 

       

 

 

On Wed, Aug 23, 2023 at 6:53 AM Brian Harris <[email protected] 
<mailto:[email protected]> > wrote:

We have a project with standpipes and a basement. All floors above the basement 
drain through the Standpipe drain and empty at grade. We usually then drain the 
remaining (basement) section of standpipe through the bottom hose valve. The GC 
is asking if we can instead drain that last section by tying into the roof 
drain in the same stairwell that runs outside below grade. Is this a no-no?

 

Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 

 


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to