We have a non-combustible, light hazard building where a steel pan roof
deck (with some non-combustible architectural finishes on the underside)
forms a balcony over a patio. The steel roof deck has a drainage slope on
top formed from combustible rigid insulation that is covered with
non-combustible roofing material – forming a
noncombustible-combustible-noncombustible sandwich. There are no exposed
combustible materials or combustible concealed spaces since all of the
materials are in direct contact.



We typically see these considered non-combustible construction and exempt
from sprinklers per NFPA 13 2016 ed 8.15.7.2, however a plans reviewer has
expressed concerns that the presence of the combustible middle layer voids
the ‘non-combustible construction’ consideration.



It seems that the code allows for the presence of some combustible
materials in the assembly based on NFPA 13 2016 ed 8.15.7.3 allowances for
combustible construction with non-combustible finishes. However, this
specific construction does not meet any of the specifically listed
exemptions.



Has anyone seen anything similar to this?



Matt