So I have a 13D residential project with a 12:12 pitch, beamed ceiling configuration. In the last beam pocket area there is a fireplace located below. It's literally impossible to place a sprinkler far enough away from the fire place per 13D's required spacing for both the ordinary or intermediate temperature sprinklers without violating the requirement to be within 36" vertically down from the peak. So it would seem I have to violate something in order to get this to work. I can either use a quick response 286F sprinkler which should cover the temperature issue but violate 13D's use of quick response sprinklers which only allows for very limited usage of such. Or I can violate the 36" down from peak requirement and use residential sprinklers for that bay. At least that's the way I see it.
Any recommendations on how to address this? Best Regards, Anthony Johnson Mountain Fire Protection 'Saving Lives and Valuing Property' <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail> Virus-free.www.avg.com <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>