Thanks, I also found this in NFPA 25. [cid:image001.png@01D9B4D2.CC82B430]
From: Fpdcdesign <fpdcdes...@gmail.com> Sent: Wednesday, July 12, 2023 2:48 PM To: Discussion list on issues relating to automatic fire sprinklers <sprinklerforum@lists.firesprinkler.org> Subject: [Sprinklerforum] Re: Old Pipe Scheduled Systems I see these all the time. 1. There is a section in 13 about water supplies for pipe schedule systems. That won’t give you something for a placard but it would tell you if there is sufficient water for it. 2. Placards are only required for hydraulically calculated systems. Several years ago, I was asked to hydraulically calculate a pipe schedule system in a school in my town. The FM was insisting on the full calc. When I went back to him and said the system in the much-gabled attic would be flowing 54 sprinklers in the 2535 sqft design area, which could not be provided by the existing system or town water supply, he changed his tune. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080<tel:860-535-2080> (ofc) 860-554-7054<tel:860-554-7054> (fax) 860-608-4559<tel:860-608-4559> (cell) On Jul 12, 2023 at 2:33 PM, <Bobby Welch<mailto:bobby.we...@koorsen.com>> wrote: I am running into a lot of old systems that do not have hydraulic placard and some of them are old pipe scheduled system. Has anyone ran into an old pipe schedule system were the fire marshal is requesting hydraulic placards and if so has anyone found a way to satisfy the requirements without surveying the entire system and running new calculations? Bobby Welch | Sprinkler Systems Designer KOORSEN FIRE & SECURITY 8090 N Dixie Dr, Dayton, OH 45414 P 937.641.8403 | Ext. 0318 | M 937.594.8457 bobby.we...@koorsen.com<mailto:bobby.we...@koorsen.com> | www.koorsen.com<http://www.koorsen.com> 24x7x365 Service: 937.660.7050 | servic...@koorsen.com<mailto:servic...@koorsen.com> _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org