I just got through doing a room with 15 ft high racks that can be moved 
side-to-side for access. Similar to a medical records storage system. In-rack 
sprinklers were not an option. I based the design on multiple row rack storage 
and used a CMSA sprinkler. There is no realistic way to provide sprinklers in 
or under a moving object.   
  

  
Since they are moveable, they should fall under 9.5.5.3.2 (2019 edition). Your 
situation sounds like it does create a space for a shielded fire so that may 
need to be taken into consideration in the ceiling design.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On May 10, 2023 at 9:50 AM,  <Matt Grise (mailto:[email protected])>  wrote:
>   
>   
>         
>   
>
> We have a cannabis grow room with racks that move 3 feet side to side along 
> tracks – to allow a dense pack of racks, but then they can move for access to 
> the plants.
>
>   
>
>   
>
>   
>
> The Fire Department would like in-racks under the top level since the plants 
> are set on large plastic trays that would block ceiling level sprinkler 
> discharge.
>
>   
>
>   
>
>   
>
> Does anyone have experience providing in-racks on moving racks? Any idea what 
> product would be suitable to provide 3’ of travel for a moving in-rack system?
>
>   
>
>   
>
>   
>
> Thanks!
>
>   
>
>   
>
>   
>
> Matt   
>
>   
>
>   
>
>   
>
>   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to