I just got through doing a room with 15 ft high racks that can be moved side-to-side for access. Similar to a medical records storage system. In-rack sprinklers were not an option. I based the design on multiple row rack storage and used a CMSA sprinkler. There is no realistic way to provide sprinklers in or under a moving object.
Since they are moveable, they should fall under 9.5.5.3.2 (2019 edition). Your situation sounds like it does create a space for a shielded fire so that may need to be taken into consideration in the ceiling design. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On May 10, 2023 at 9:50 AM, <Matt Grise (mailto:[email protected])> wrote: > > > > > > We have a cannabis grow room with racks that move 3 feet side to side along > tracks – to allow a dense pack of racks, but then they can move for access to > the plants. > > > > > > > > The Fire Department would like in-racks under the top level since the plants > are set on large plastic trays that would block ceiling level sprinkler > discharge. > > > > > > > > Does anyone have experience providing in-racks on moving racks? Any idea what > product would be suitable to provide 3’ of travel for a moving in-rack system? > > > > > > > > Thanks! > > > > > > > > Matt > > > > > > > > > > > _________________________________________________________ SprinklerForum > mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to [email protected] >
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]