We have a project that is a warehouse building protected with ESFR sprinkler 
heads, the warehouse area has 6'x6' skylights spaces about 50' apart. The 
skylights is only about 8" above the metal deck of the warehouse ceiling. The 
ESFR heads are spaced 10'x10' with the skylight directly in the middle of the 
lines.

We are wondering if we need to provide protection in these skylights, common 
sense says the size and depth would not delay the operation of the sprinkler 
heads, so no heads should be required. Code says skylights over 32 ft² require 
sprinkler protection.

If we need to protect the skylight do we use an ESFR heads or can you use a 
Q.R. standard spray heads. The ESFR head if installed would stick below the 
plane on the warehouse ceiling and would now be too close to the other heads 
and would cold solder them.

Comments, ideas.

We are using NFPA #13 2013ed.

Thank You