This topic is covered in NFPA 13 -2022 edition:
28.2.4.7.3*
<https://link.nfpa.org/publications/13/2022/annexes/A/groups/28#ID000130009750>


The requirements of 28.2.4.7.1
<https://link.nfpa.org/publications/13/2022/chapters/28#ID000130004847> and
28.2.4.7.1.1
<https://link.nfpa.org/publications/13/2022/chapters/28#ID000130004848> to
include every sprinkler in the design area shall not apply where sprinklers
are provided above and below obstructions.
28.2.4.7.3.1

Sprinklers under the obstruction shall not be required to be included in
the hydraulic calculation of the ceiling sprinklers.
ENHANCED CONTENT
Collapse

The basic idea behind hydraulic calculations, including reasonable safety
factors, is to account for all the sprinklers that might open in case of a
fire. Where sprinklers are installed both above and below obstructions, all
sprinklers above and below the obstructions are unlikely to open. Rather
than force the user to calculate both sets of sprinklers simultaneously,
the user is directed to prove the most demanding situation with
calculations. In most cases, ceiling sprinklers will represent the greatest
demand, unless significant numbers of sprinklers are installed under
obstructions with long runs of relatively small-diameter pipe.

The presence of a permanent or temporary obstruction, such as an overhead
garage door, is treated in a manner similar to that for a ceiling
configuration that requires sprinklers to be located above and below the
ceiling.
28.2.4.7.3.2

Where the piping to sprinklers under obstructions follows the same sizing
pattern as the branch lines, no additional hydraulic calculations shall be
required for sprinklers under obstructions.
ENHANCED CONTENT
Collapse

The requirement in 28.2.4.7.3.2 clarifies that as long as the pipe sizing
under the obstruction is the same as the branch lines, the sprinklers under
the obstruction generally will not be more demanding because of the
increased elevation head gained dropping down under the obstruction. Care
still should be taken, however, where long runs of pipe are utilized to
provide protection under an obstruction, where multiple sprinklers are fed
off a single drop, and where the drop is a dead-end feed off a gridded
overhead system.
The 2025 edition of NFPA 13 might have some additional guidance on this
issue.  The first draft meetings were just held last month,

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*


Don’t gamble; attend AFSA41!

Click here <https://www.firesprinkler.org/register-for-afsa41/> to view the
schedule and register for AFSA41: Convention, Exhibition, and Apprentice
Competition at the Bellagio Las Vegas October 16-19, 2022. The regular
registration deadline is August 26, 2022.


On Tue, Aug 23, 2022 at 3:34 PM Fpdcdesign <[email protected]> wrote:

> What I have is an ESFR system where i need to add a single sprinkler in 2
> locations under ducts. 23.4.4.7.3.1 states that sprinklers under
> obstructions do not need to be included in hydraulic calculations.
> 23.4.4.7.3.2 states that if the sprinklers are under obstructions are piped
> with the same size branch piping, additional calculations under
> obstructions are not required.  I’m assuming that the difference is that
> the first one is based on one or two sprinklers under obstructions in
> isolated location. The other is if enough sprinklers are installed under
> obstructions to create an new calculation area. Neither really address any
> restrictions on pipe sizes for sprinklers under obstruction.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>
>
> On Aug 23, 2022 at 12:35 PM, <Derrek Crigler <[email protected]>>
> wrote:
>
> NPFA 13 2016 23.4.4.7.3.2
>
>
>
> *From:* Fpdcdesign <[email protected]>
> *Sent:* Tuesday, August 23, 2022 9:30 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: Sizing of pipe below obstructions
>
>
>
> Brett, any specific reference for that?
>
>
>
>
>
>
> On Aug 23, 2022 at 12:21 PM, <Brett Peters <[email protected]>> wrote:
>
> Typically non storage sprinkler supplied with 1"
>
> Storage type sprinkler supplied with same size as branch line (typical for
> ESFR sprinklers)
>
>
>
> Thanks
>
>
>
> Brett Peters
>
> General Manager Installation & Design
>
> Proudline Fire Protection Services Ltd.
>
> [email protected]
>
> 780 490 7602 office ext 202
>
> 780 490 7605 fax
>
> 780 777 0568 cell
>
> 780 718 2676 24h
>
> Visit us at www.proudline.ca
>
>
>
> Proudline now offers ULc listed monitoring services, please contact
> [email protected] for more information
>
>
>
>
>
>
>
>
>
>
>
>
>
> On Tue, Aug 23, 2022 at 10:09 AM Fpdcdesign <[email protected]> wrote:
>
>
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054  (fax)
>
> 860-608-4559 (cell)
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org