13 2019 edition states: 
9.5.4.1.3 
For ceilings that have insulation installed directly against underside of the 
ceiling or roof structure, the deflector distance shall be measured from the 
bottom of the insulation and shall be in accordance with 9.5.4.1.3.1, 
9.5.4.1.3.2, and 9.5.4.1.3.3.

9.5.4.1.3.1 
Insulation used to measure sprinkler deflector distance shall be batt 
insulation or insulation that withstands 3 lb/ft2 (0.13 kg/m2) uplift force.

9.5.4.1.3.2 
For insulation that is installed directly against the ceiling or roof structure 
and is installed flat and parallel to the ceiling or roof structure, the 
deflector distance shall be measured to the underside of the insulation.

To me up to 12" would be a compliant installation as long as the insulation is 
batt type which I presume it would have to be based on description.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Scott Harvey via Sprinklerforum
Sent: Wednesday, February 16, 2022 9:18 AM
To: [email protected]
Cc: Scott Harvey <[email protected]>; Prahl, Craig/GVL 
<[email protected]>
Subject: Re: [EXTERNAL] Obstructed vs Unobstructed Construction

 
BE ADVISED - This email originated outside EMCOR. 
 

Craig, the joists are 12” deep, 16” o.c.  The entire depth and width of the 
joist is filled with noncombustible insulation. 

Sent from my iPhone

> On Feb 16, 2022, at 6:55 AM, Prahl, Craig/GVL via Sprinklerforum 
> <[email protected]> wrote:
> 
> What are the depths of the joists, the depth of the insulation and the 
> spacing between the joists?
> 
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
> [email protected] | 
> https://urldefense.com/v3/__http://www.jacobs.com__;!!FaxH778!NpU3BJxYKauVH0bhPEdX1FAnTug5yROhXr9YqwVi7O2ZEKWL_FHKv8ML1fPCtDke$
>  
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: email or MS TEAMS
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Scott Harvey via Sprinklerforum
> Sent: Wednesday, February 16, 2022 12:53 AM
> To: [email protected]
> Cc: Scott Harvey <[email protected]>
> Subject: [EXTERNAL] Obstructed vs Unobstructed Construction
> 
> Hi all, I have a question for the group.
> 
> I've got a storeroom, ceiling is open to structure.  The roof structure is 
> solid wood joists, which are fully insulated between each joist.
> 
> We have installed standard spray upright sprinklers with the deflectors 
> approx 8-10 inches below the bottom of the joist/insulation.
> 
> In my mind, this is unobstructed construction, because per 
> "A.https://urldefense.com/v3/__http://8.5.4.1__;!!FaxH778!NpU3BJxYKauVH0bhPEdX1FAnTug5yROhXr9YqwVi7O2ZEKWL_FHKv8ML1eJeTxOh$
>   Batt insulation creates an effective thermal barrier and can be considered 
> the ceiling/roof deck when determining distances between deflector and 
> ceiling."  Chapter 3 defines Obstructed Construction "Panel construction and 
> other construction where beams, trusses, or other members impede heat flow or 
> water distribution in a manner that materially affects the ability of the 
> sprinkler to control or suppress a fire".
> 
> Now that I look at this again, I'm thinking I am wrong and should be 
> obstructed construction because although the batt insulation creates a 
> thermal barrier (similar to a smooth ceiling) the structure is still the 
> same, so I would need to keep my upright sprinklers max 6-inches below the 
> bottom of structure?
> 
> Would appreciate input from the group.
> 
> 
> Thanks,
> 
> Scott Harvey, CET
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WNJbuEDrG9DqZDyEL512vMojwZ-VOZeVutCjsR6asnXWsu5WOOUl9NA1aE0ZoG95hg$
> 
> ________________________________
> 
> NOTICE - This communication may contain confidential and privileged 
> information that is

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!NpU3BJxYKauVH0bhPEdX1FAnTug5yROhXr9YqwVi7O2ZEKWL_FHKv8ML1Rr_halt$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to