Here are both tables from the 1978 edition.  If they don't come through, hit me 
up via email

It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com<http://www.sprinkleracademy.com>
[email protected]<mailto:[email protected]>
??
OUR STUDENTS SAVE LIVES!!

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Fpdcdesign via Sprinklerforum <[email protected]>
Sent: Tuesday, February 8, 2022 8:06 AM
To: Sprinklerforum <[email protected]>
Cc: Fpdcdesign <[email protected]>
Subject: Re: NFPA 13, 1978 Table 2.2.1 (B)




  I have 1980 if you need that. There was a minor change between 1975 and 1980 
in the tabular data, but other than tat, they are the same.



 Todd G Williams, PE
Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (tel:860-535-2080)  (ofc)

860-554-7054 (tel:860-554-7054)     (fax)

860-608-4559 (tel:860-608-4559)  (cell)







>
> On Feb 8, 2022 at 8:56 AM,  <Craig/GVL via Sprinklerforum Prahl 
> (mailto:[email protected])>  wrote:
>
>
>
>  I'm in the middle of a whse renovation project study and the original design 
> used NFPA 231, it references 1978 NFPA 13, Table 2.2.1(B). Would anyone have 
> a copy of the 1978 NFPA 13 and could send me a snapshot of that Table? I've 
> looked on the NFPA site and they don't have versions available that far back. 
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
> [email protected] | www.jacobs.com<http://www.jacobs.com> 1041 East 
> Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS 
> ________________________________ NOTICE - This communication may contain 
> confidential and privileged information that is for the sole use of the 
> intended recipient. Any viewing, copying or distribution of, or reliance on 
> this message by unintended recipients is strictly prohibited. If you have 
> received this message in error, please notify us immediately by replying to 
> the message and deleting it from your computer. 
> _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to