Matt,

I haven't dealt with that situation in real life, but have in theory had 
several conversations about it. I am in agreement with you that this should be 
allowable per the code language. You never exceed 110 s.f. and the average 
ACTUAL FLOOR AREA (not SxL) does not exceed 100 s.f.

-Kyle M

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Tuesday, January 18, 2022 8:22 AM
To: [email protected]
Cc: Matt Grise <[email protected]>
Subject: [EXTERNAL] RE: ESFR obstruction shift

No - since we are moving along the line, when one space goes from 10 to 11, the 
space on the other side goes from 10' to 9'

Matt 


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matthew J Willis via Sprinklerforum
Sent: Tuesday, January 18, 2022 9:00 AM
To: [email protected]
Cc: Matthew J Willis <[email protected]>
Subject: RE: ESFR obstruction shift

Are you not creating a 10x11 situation since you are moving every other 
sprinkler?

If so, you may be violating the 100 sq ft per average requirement for moved and 
adjacent?

R/
Matt

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Tuesday, January 18, 2022 6:00 AM
To: [email protected]
Cc: Matt Grise <[email protected]>
Subject: ESFR obstruction shift

I am looking at a warehouse layout where we can get a very nice head pattern by 
laying the heads out 10ft by 10ft, and then shifting the ones that land near 
joists 1ft along the line as allowed by NFPA 13.

The only issue is that we have to shift every other head. Making a 9ft - 11ft 
pattern along the branch line. As far as I can tell, this meets the letter of 
the code, but it seems like a stretch.

Has anyone come across a similar situation where so many heads needed to be 
shifted to avoid roof structures?

Matt

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,l1exGGqk0cDcPNoSdqRWtD1YmZdqStCzx0CUF-Olhi1rqB9Iz8Fn6d7eBTNXNMfF8T-7GZY94qom2OweTyV4Gyin1hiL-CJ82tDF4yhwF7g0ofhpr4fwsNalRZM,&typo=1__;JSUlJSU!!Ba8_KKAT!eogk1pEssHmJtaZHhoNM1xMOrahW4a40OEoiC7xHQPIDjpwV0fnvj8Sfjpv8d1bFGzI$
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,faagUYTvRqNofSbZjC709kxTbRDQVTelhUkbtQ0AWq4V349KeRLZVnCRia1Vjt6yQqBjB_beLshOylNEy-3N0UIJJJFKTWvWeUpRcWUx-0A,&typo=1__;JSUlJSU!!Ba8_KKAT!eogk1pEssHmJtaZHhoNM1xMOrahW4a40OEoiC7xHQPIDjpwV0fnvj8Sfjpv8sH-n2sk$
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!Ba8_KKAT!eogk1pEssHmJtaZHhoNM1xMOrahW4a40OEoiC7xHQPIDjpwV0fnvj8Sfjpv8Su2SCv4$
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to