Negative.

Check 10.2.2 same edition (10)

R/
Matt

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Trillium Fire Sprinkler Design INC via Sprinklerforum
Sent: Tuesday, January 11, 2022 2:05 PM
To: [email protected]
Cc: Trillium Fire Sprinkler Design INC <[email protected]>
Subject: RE: COMBUSTIBLE CONCEALED SPACE

My question is: Are QR uprights listed to be used in those areas or does it 
have to be a CCS sprinkler?

Troy

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Tom Wellen via Sprinklerforum
Sent: January 11, 2022 3:56 PM
To: [email protected]
Cc: Tom Wellen <[email protected]>; Trillium Fire Sprinkler Design INC 
<[email protected]>
Subject: Re: COMBUSTIBLE CONCEALED SPACE

Troy,

No. NFPA 13, 2019 edition in 9.3.2 is specific that sprinklers are listed for 
horizontal combustible concealed spaces. Specifically listed to provide 
protection.....




On Tue, Jan 11, 2022 at 2:40 PM Trillium Fire Sprinkler Design INC via 
Sprinklerforum <[email protected]> wrote:

> Can someone confirm that it is not mandatory to use CCS sprinklers in 
> a space 36" or less?
>
>
>
> I know it allows for larger spacing, but code wise. I don't believe 
> they are a must and the space can be protected with QR uprights.
>
>
>
> Regards
>
>
>
> Troy S
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>


--
Tom Wellen - May '91
Senior Fire Protection Consultant
Fire Engineering & Consulting, LLC
(972) 355-2159
fireeac.com

<http://fireeac.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to