Yep, typically end up with K22's down the center at the peak, with a K17 sandwich to the outside. Jamie Seidl
On Fri, Dec 24, 2021 at 1:41 PM Mike Hairfield via Sprinklerforum < [email protected]> wrote: > Here is the situation: > > Building has 40'-8" Maximum Ceiling height at the ridge, the building is > designed with K16.8 ESFR's. > > Can the areas that are over the 40'-0" maximum ceiling height be designed > using K22.4 or K25.2 ESFR's > and be approved? > > Thanks, > > Mike Hairfield > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org