Yep, typically end up with K22's down the center at the peak, with a K17
sandwich to the outside.
Jamie Seidl

On Fri, Dec 24, 2021 at 1:41 PM Mike Hairfield via Sprinklerforum <
[email protected]> wrote:

> Here is the situation:
>
> Building has 40'-8" Maximum Ceiling height at the ridge, the building is
> designed with K16.8 ESFR's.
>
> Can the areas that are over the 40'-0" maximum ceiling height be designed
> using K22.4 or K25.2 ESFR's
> and be approved?
>
> Thanks,
>
> Mike Hairfield