§Joe,
I'm not clear on which edition of NFPA 13 is in force for you, however I
would look closely at the parameters of §9.5.5.3, inclusive, and the
annex material for those sections in the '19 edition, and into
§10.2.7.2.1.1.
I looked into the '19 handbook, and found the following in the "blue"
text below §9.5.5.3:
/Once the sprinkler discharge pattern is developed, obstructions in
the horizontal plane can prevent the//
//sprinkler discharge from reaching the protected hazard. In some
situations, the obstruction cannot be//
//avoided, and additional sprinklers are necessary to compensate for
areas under the obstruction that would//
//not receive adequate coverage./
Reading further, I found the following blue text below §10.2.7.2.1.2
[all emphasis is mine]:
/Large, solid continuous obstructions were previously referred to as
horizontal obstructions. These obstructions,//such as deep beams or
a large duct mounted on or very near the ceiling, significantly
affect discharge //patterns and must be located above the sprinkler
discharge pattern in accordance with 10.2.7.2.1.2./ /Smaller
continuous obstructions, _*such as pipes*_ and bottom members of
trusses, and noncontinuous //obstructions, such as the web members
of bar joists located within 18 in. (450 mm) below the sprinkler,
//should be in compliance with the requirements of 10.2.7.2.1.1./
My read on this is that if the obstruction is at least 18" below the
sprinkler deflector, and is not more than 48" wide, whatever it is
doesn't create an obstruction to discharge.
hope that helps,
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 12/16/2021 10:29 AM, Joe Burtell via Sprinklerforum wrote:
I apologize if this has already been asked and answered. I could have sworn
NFPA addressed this but I am looking for when a group of mechanical pipes
are racked and create a wide obstruction, what the minimum gaps between
pipe to not consider it a solid obstruction? Can someone point me to the
correct section, please?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email:[email protected]
Web Site:http://www.burtellfire.com
*“**The bitterness of poor quality remains long after the sweetness of low
price is forgotten.**”*
*NOTICE:* The information contained in this e-mail transmission is
intended only for use of the individual or entity named above. This e-mail
transmission, and any documents, files, previous e-mail transmissions or
other information attached to it, may contain confidential information that
is legally privileged. If you are not the intended recipient of this
e-mail transmission, or the employee or agent responsible for delivering it
to the intended recipient, you are hereby notified that any disclosure,
dissemination, distribution, copying or other use of this transmission or
any of the information contained in or attached to this e-mail is strictly
prohibited. If you have received this e-mail transmission in error, please
immediately notify us by return e-mail transmission and destroy the
original e-mail transmission as well as its attachments without reading or
saving it in any manner. Thank you.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org