I have searched the from the deepest depths to the highest heights within NFPA 
13 for a solution and am coming up empty.

We have a freezer warehouse, storing packaged meats on foam trays which are 
placed in plastic trays. The frozen meat per NFPA 13 is a class III, the kicker 
is the exposed, expanded plastic tray which represents about 63% of the package 
load.  They claim to only put about 2.5 lbs of meat in a plastic tray that 
weighs 4.4 lbs.  This is pushing us into considering this as a Group A plastic 
commodity.

I have found no system criteria for a freezer warehouse with 22' of racked 
storage and a 30 ft ceiling/roof height and exposed, unexpanded group A 
plastic.  Any options we find show them as being Wet systems only.

I am starting to dig into the FM data sheets but was looking to see if anyone 
has any insight or if I've missed some option hidden away in the dark corners 
of NFPA 13.

Quell only goes up to Class III commodities.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to