Somewhat for my own information, is fluid delivery time calculation required 
now? My understanding was that it is one option, but that a system over 750 
gallons with a quick opening device just has to meet the 60 second water 
delivery time after instal.  Obviously doing the calculation ensures that, but 
you can still install it and take the gamble right? We do not do very many over 
750 because we would prefer not to get into that issue but I just want to be 
sure I understand this correctly as much as anything.


Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]

[Image]

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Travis Mack via Sprinklerforum <[email protected]>
Sent: Monday, November 1, 2021 9:43:37 AM
To: [email protected] 
<[email protected]>
Cc: [email protected] <[email protected]>
Subject: Re: Dry System Size


BE ADVISED - This email originated outside EMCOR.


Tyco FDT is only software for this.


Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700<tel:480-505-9271;700> C: 480-272-2471<tel:480-272-2471>

[email protected]<mailto:[email protected]>

https://urldefense.com/v3/__http://www.mfpdesign.com__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7GrefwvE$
 
<https://urldefense.com/v3/__http://www.mfpdesign.com/__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7ELxnuHV$
 >



Send large files to us via: 
https://urldefense.com/v3/__https://www.hightail.com/u/MFPDesign__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7DajYf-l$
 
<https://urldefense.com/v3/__https://na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7Ilxk3Ks$
 >

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Brian Harris via Sprinklerforum <[email protected]>
Sent: Monday, November 1, 2021 6:42:38 AM
To: [email protected] 
<[email protected]>
Cc: Brian Harris <[email protected]>
Subject: Dry System Size

I assume with a dry system size of 1200 gallons my options are to add a 2nd dry 
valve and have (2) 600 gallon system with quick opening devices or run delivery 
time calc's and see if by chance it's under 60 seconds? If the latter is true 
what do most use to run theses calc's?

Brian Harris, CET
BVS Systems Inc.
Design Manager
https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7Nje7aIR$
 
<https://urldefense.com/v3/__http://bvssystemsinc.com/__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7BMIYZpt$
 
<https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7Nje7aIR$
 >>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7GD1H7e4$
 
<https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7GD1H7e4$
 >
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!MZj3OknLdxHhGXNWbKKkGOgcBnPa4tEtNFevAt65hmUkKBSEsb8jGUYc7GD1H7e4$

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to