Is the dry system water delivery software capable of modeling this 
configuration, using a given water supply?

Best.

Bruce Verhei


> On 10/27/2021 9:50 AM Kevin Hall via Sprinklerforum 
> <[email protected]> wrote:
> 
>  
> If the pipe marked in red is removed and capped off, it eliminates any
> split flows/transfer lines on the branch lines. So with the red pipe
> removed I would define it as a tree. With the red pipe installed, I would
> define it as a grid.
> 
> The above is my opinion and has not been processed as a formal
> interpretation in accordance with the NFPA Regulations Governing Committee
> Projects. This is provided with the understanding that the AFSA assumes no
> liability for this opinion or actions taken on it and they are not to be
> considered the official position of the NFPA or its technical committees.
> AFSA cannot provide design or consulting engineering services, and this
> opinion should therefore not be considered, nor relied upon, as such.
> 
> 
> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> 
> Coordinator, Engineering and Technical Services
> 
> American Fire Sprinkler Association
> 
> [email protected]
> 
> 214-349-5971
> 
> 
> On Wed, Oct 27, 2021 at 12:47 PM J H via Sprinklerforum <
> [email protected]> wrote:
> 
> > So, for discussions sake take a look at the image link - what would you all
> > call this system? I have my opinion but I don't see how it's much different
> > than Ed's original drawing:
> > https://ibb.co/xSW04dj
> >
> > On Wed, Oct 27, 2021 at 9:46 AM J H <[email protected]> wrote:
> >
> > > So, for discussions sake take a look at the image link - what would you
> > > all call this system? I have my opinion but I don't see how it's much
> > > different than Ed's original drawing:
> > > https://ibb.co/xSW04dj
> > >
> > > On Wed, Oct 27, 2021 at 9:40 AM Kevin Hall <[email protected]>
> > > wrote:
> > >
> > >> Yes, I see that now... looks like I have another PI to add to the NFPA
> > 13
> > >> list. Look for that line of sprinklers to be removed in the 2025 edition
> > >> haha.
> > >>
> > >> The above is my opinion and has not been processed as a formal
> > >> interpretation in accordance with the NFPA Regulations Governing
> > Committee
> > >> Projects. This is provided with the understanding that the AFSA assumes
> > no
> > >> liability for this opinion or actions taken on it and they are not to be
> > >> considered the official position of the NFPA or its technical
> > committees.
> > >> AFSA cannot provide design or consulting engineering services, and this
> > >> opinion should therefore not be considered, nor relied upon, as such.
> > >>
> > >>
> > >> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> > >>
> > >> Coordinator, Engineering and Technical Services
> > >>
> > >> American Fire Sprinkler Association
> > >>
> > >> [email protected]
> > >>
> > >> 214-349-5971
> > >>
> > >>
> > >> On Wed, Oct 27, 2021 at 12:19 PM J H via Sprinklerforum <
> > >> [email protected]> wrote:
> > >>
> > >>> Kevin,
> > >>> That's true for most of the sprinklers in the diagram but look at
> > figure
> > >>> A.3.3.206.6 (2019) - the farthest loop from the supply has sprinklers
> > on
> > >>> it
> > >>> and it's connecting both loops - those sprinklers are receiving water
> > >>> from
> > >>> two mains. Likewise, per the definition of a main the only main in Ed's
> > >>> example is the center line. Everything else are looped branchlines per
> > >>> the
> > >>> definitions.
> > >>>
> > >>> JH
> > >>>
> > >>>
> > >>> On Wed, Oct 27, 2021 at 9:09 AM Kevin Hall via Sprinklerforum <
> > >>> [email protected]> wrote:
> > >>>
> > >>> > The annex shows the branch lines fed by the cross main from two
> > >>> directions,
> > >>> > the sprinkler can still only receive water from one direction from
> > the
> > >>> > branch line... that is the distinction in the definition.
> > >>> >
> > >>> > The above is my opinion and has not been processed as a formal
> > >>> > interpretation in accordance with the NFPA Regulations Governing
> > >>> Committee
> > >>> > Projects. This is provided with the understanding that the AFSA
> > >>> assumes no
> > >>> > liability for this opinion or actions taken on it and they are not to
> > >>> be
> > >>> > considered the official position of the NFPA or its technical
> > >>> committees.
> > >>> > AFSA cannot provide design or consulting engineering services, and
> > this
> > >>> > opinion should therefore not be considered, nor relied upon, as such.
> > >>> >
> > >>> >
> > >>> > Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> > >>> >
> > >>> > Coordinator, Engineering and Technical Services
> > >>> >
> > >>> > American Fire Sprinkler Association
> > >>> >
> > >>> > [email protected]
> > >>> >
> > >>> > 214-349-5971
> > >>> >
> > >>> >
> > >>> > On Wed, Oct 27, 2021 at 12:05 PM J H via Sprinklerforum <
> > >>> > [email protected]> wrote:
> > >>> >
> > >>> > > I have a problem with the simplified definition floated out here
> > >>> that a
> > >>> > > grid system is one that feeds a sprinkler from two directions
> > >>> because of
> > >>> > > the illustration of a looped system in the annex of '13 which shows
> > >>> > > sprinklers attached to the end portion of the loop resulting in
> > those
> > >>> > > sprinklers receiving water from two directions. Technically the
> > only
> > >>> > cross
> > >>> > > main is the center piping - everything else are looped
> > branchlines. I
> > >>> > would
> > >>> > > be prepared for kickback from a knowledgeable AHJ. I would
> > personally
> > >>> > avoid
> > >>> > > a design like this if at all possible to avoid the headache of
> > >>> hashing it
> > >>> > > out w/ an AHJ. But if it's the difference between a system like
> > this
> > >>> and
> > >>> > a
> > >>> > > fire pump it might be worth the fight.
> > >>> > >
> > >>> > > JH
> > >>> > >
> > >>> > > On Wed, Oct 27, 2021 at 6:04 AM Sean Conlin via Sprinklerforum <
> > >>> > > [email protected]> wrote:
> > >>> > >
> > >>> > > > If you were to put caps on the left and right lines going north
> > and
> > >>> > > south,
> > >>> > > > it resembles a compound gridded system and a sprinkler can
> > receive
> > >>> > water
> > >>> > > > from both sides.
> > >>> > > >
> > >>> > > > The east and west lines are essentially the mains and so is the
> > 4"
> > >>> in
> > >>> > the
> > >>> > > > middle.
> > >>> > > >
> > >>> > > > Yes is has a looped piping  arrangement and is symmetrical but it
> > >>> is a
> > >>> > > > gridded system by NFPA-13 definition.  If you were to not tie the
> > >>> lines
> > >>> > > > together, it would be a loop.
> > >>> > > >
> > >>> > > > Regards,
> > >>> > > >
> > >>> > > > Sean W. Conlin
> > >>> > > > E:[email protected]
> > >>> > > >
> > >>> > > > This message, including any attachments is considered
> > confidential
> > >>> and
> > >>> > > for
> > >>> > > > use only by the intended recipient(s).
> > >>> > > > Any other distribution, copying or disclosure is strictly
> > >>> prohibited.
> > >>> > > > Please delete this communication and notify
> > >>> > > > Demand Sprinkler Design Inc. if you are not the intended
> > recipient
> > >>> or
> > >>> > > have
> > >>> > > > received this message in error. Demand
> > >>> > > > Sprinkler Design Inc. accepts no responsibility or liability for
> > >>> any
> > >>> > loss
> > >>> > > > or damage from use, including damage from viruses.
> > >>> > > >
> > >>> > > > -----Original Message-----
> > >>> > > > From: Ed Kramer <[email protected]>
> > >>> > > > Sent: October 26, 2021 1:31 PM
> > >>> > > > To: [email protected]
> > >>> > > > Subject: Gridded dry system
> > >>> > > >
> > >>> > > > Is this sprinkler system a gridded system?   I've avoided this
> > >>> type of
> > >>> > > > design in the past for dry systems because it 'kinda' a grid, but
> > >>> not
> > >>> > > > really.  Now I'm questioning my questioning.  What are your
> > >>> thoughts?
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> > > > Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> >
> > >>>
> > https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?dl=0
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> > > > Ed Kramer
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> > > >
> > >>> > > > _______________________________________________
> > >>> > > > Sprinklerforum mailing list
> > >>> > > > [email protected]
> > >>> > > >
> > >>> > > >
> > >>> > >
> > >>> >
> > >>>
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>> > > >
> > >>> > > _______________________________________________
> > >>> > > Sprinklerforum mailing list
> > >>> > > [email protected]
> > >>> > >
> > >>> > >
> > >>> >
> > >>>
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>> > >
> > >>> > _______________________________________________
> > >>> > Sprinklerforum mailing list
> > >>> > [email protected]
> > >>> >
> > >>> >
> > >>>
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>> >
> > >>> _______________________________________________
> > >>> Sprinklerforum mailing list
> > >>> [email protected]
> > >>>
> > >>>
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>
> > >>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to