Here are some Victaulic video links of the shake, rattle and roll.

https://youtu.be/tPaRcqt4qPI
https://youtu.be/xsG8_Nz-ym4
https://youtu.be/5ro8SnECHQU


On Tue, Oct 19, 2021 at 2:54 PM Steve Leyton via Sprinklerforum <
[email protected]> wrote:

> I appreciate the overview and wagering strategy but the SEOR is a friendly
> on this one and  there's nothing conventional about this application.  It's
> a tunnel, 40' below the street that communicates from one building to
> another across two public streets  and an intervening block in DT San
> Diego.   And crosses a fault, so a high likelihood of short waveform
> movement if there's ever an event.   So we have the fault zone, the two
> building basement crossings and some other flexure points that we're trying
> to resolve.    On top of all that,  it's highly secure and there's limited
> space  above detention-grade ceilings, so the required clearances for
> movement apparently can't be fully realized.   The contractor has expressed
> a preference for the multiple 90s on this one because of space constraints
> and since this is a very sensitive project and everyone is earnestly
> working to get it right, I've been tasked with establishing what range of
> vertical movement the detail in the NFPA figure is capable of.  Also trying
> to verify if it's been field tested (it has, apparently) and whether it's
> been lab tested or whether there is any particular requirement for vertical
> movement specifically.   The language of 9.3.3.2 is confusing, with
> reference made to open and closing of the joint and also to, "...movement
> relative to the separation in the other two dimensions..."    What "other
> two dimensions", time and space?
>
> SML
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of AKS-Gmail-IMAP via Sprinklerforum
> Sent: Tuesday, October 19, 2021 12:02 PM
> To: [email protected]
> Cc: AKS-Gmail-IMAP <[email protected]>
> Subject: Re: Seismic joint detail
>
>  If we are referring to the six flexible coupling seismic separation
> assembly that every contractor finds an alternative, make a sizable wager
> with the structural engineer that the assembly provides vertical movement.
> Make sure the winnings cover the cost of six ½” pvc fittings and a four
> foot stick of ½” pvc pipe. Make the thing up and fool with it for some time
> before you present your case so that you can move it around to show it off
> like you know what you are doing, because at first it might look awkward
> enough that the engineer will cry foul. By the way, the details for this
> six coupling assembly show vertical accommodation in the elevation detail.
>  You might obfuscate the demonstration by asking how much differential
> seismic movement this engineer is really expecting. Differential seismic
> lateral motion is due to how easy it is for one structural building section
> to be different in lateral flexibility than the next building section, i.e.
> across the seismic separation joint. Each building section will wiggle
> differently than the next. The difference shows up at the joint. Vertical
> differential flexibility, in other words “pogoing” differently than the
> next structural section is not happening very much, if any. Buildings are
> relatively much more vertically stiff than they are horizontally stiff. I
> might bet the structural engineer has not tried to calculate this. What
> might be the case, like this building is in Houston Texas which I believe
> has more seismic faults going on than any other US city, is that the
> structural engineer knows the building project has to span a known fault
> and so the structure is actually anticipating differential vertical
> movement at the joint.
> Allan Seidel
> St. Louis, MO
>
> > On Oct 19, 2021, at 11:45 AM, Steve Leyton via Sprinklerforum <
> [email protected]> wrote:
> >
> > A question was raised by a project structural engineer about the NFPA 13
> seismic joint detail shown in Fig. A.9.3.3(a), 2016 edition for reference.
>   Does anyone know if this configuration has ever been tested/measured?
>  Has it been verified as an acceptable OMNI-DIRECTIONAL solution?    The
> engineer in question is looking at the detail and in his judgement, it's
> only a 2D solution.   There are lateral and longitudinal movements shown,
> but not a vertical one.    If there are installation or hanger/bracing
> committee people who can chime in, I'm wondering if this figure has been
> vetted and that's why it's still in the standard.   Bottom line:  Is Fig.
> A.9.3.3(a) equivalent to a listed seismic loop?
> >
> >
> > Steve Leyton, President
> > Protection Design and Consulting
> > T  |  619.255.8964 x 102  |
> > www.protectiondesign.com<http://www.protectiondesign.com/>
> > 2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108 Fire
> > Protection System Design | Consulting | Planning | Training
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>


-- 
Tom Wellen - May '91
Senior Fire Protection Consultant
Fire Engineering & Consulting, LLC
(972) 355-2159
fireeac.com

<http://fireeac.com/>