Mike-
I've never designed a job that was fed from a water tank and wanted to make 
sure I covered all the bases. Thanks for your help.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Tuesday, October 19, 2021 12:10 PM
To: [email protected]
Cc: Mike Morey <[email protected]>
Subject: RE: Water Tank & Refill Rates

22 (2018 4.2.1.4 specifically) states "fire protection volume" regarding the 8 
hour fill time, since your fire protection volume is just your design flow x 
duration (30 minutes in this case) your 33gpm pump can refill the fire 
protection volume in just over 2 hours assuming you don't need to pick up the 
hose from the tank but also aren't taking any area reduction etc.  The fact 
that it would take a little over 8 to fill the entire tank shouldn't be 
relevant, since I'm guessing that may be the concern?

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Tuesday, October 19, 2021 11:44 AM
To: [email protected]
Cc: Brian Harris <[email protected]>
Subject: Water Tank & Refill Rates

 
BE ADVISED - This email originated outside EMCOR. 
 

We are looking at a project for a scout camp. They're building a new rec. hall 
and want to protect it per NFPA-13 for LH occupancy. They currently have an 
18,000-gallon water tank that is fed from a well that has a 33 gpm pump. This 
tank is dedicated for fire suppression use only and sits "uphill" from the job 
site. Is refill rate even an issue since the tank is so oversized?

Brian Harris, CET
BVS Systems Inc.
Design Manager
https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!Ol1I60Bx2fuLbBC1G4Fu7ijf4wW4wJCczWuRO5zFSC1EgSfejiBe4m7jhlrLX6tF$
 
<https://urldefense.com/v3/__http://bvssystemsinc.com/__;!!FaxH778!Ol1I60Bx2fuLbBC1G4Fu7ijf4wW4wJCczWuRO5zFSC1EgSfejiBe4m7jhpyd6yl7$
 >
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Ol1I60Bx2fuLbBC1G4Fu7ijf4wW4wJCczWuRO5zFSC1EgSfejiBe4m7jhlhc6PZs$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to