Subject: RE: Minimum Pipe Size
BE ADVISED - This email originated outside EMCOR.
I know there is a code I can't find it in NFPA 13.
Bobby Welch | Sprinkler Systems Designer KOORSEN FIRE & SE
://www.koorsen.com>
24x7x365 Service: 937.660.7050 | servic...@koorsen.com
From: travis.m...@mfpdesign.com
Sent: Wednesday, September 29, 2021 10:10 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bobby Welch
Subject: RE: Minimum Pipe Size
Been there for ages. 1" for steel pipe. ¾&qu
C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
From: Sprinklerforum On Behalf
Of Bobby Welch via Sprinklerforum
Sent: Wednesday, September 29, 2021 7:08 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bobby Welch
Subject: Minimum Pipe Size
Is there a minimum pi
Is there a minimum pipe size in NFPA 13 for sprinkler systems?