Wrenches,
Questions: Does the PV GEC have to be bonded to the ground electrode system at
the same point as the utility service equipment GEC? Is there a code section to
back this up?
Additional info:
1. The DC side of the inverter is a separately derived system and
therefore needs a GE
ilding inspector" Lafferty
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szrom
Sent: Thursday, August 19, 2010 7:38 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] PV GEC to the
My 2 cents on this issue which I have encountered on numerous occasions. Here
in NYC the majority of service switch installs agree with the convention of
BLACK, RED, BLUE. However, I have seen a few older service switches with the
reverse, BLUE, RED, BLACK.
The only documented place I have ever
(A) Mounting. Electrical equipment shall be firmly secured to the
surface on which it is mounted.
Has anyone ever had a problem with this during an inspection?
Thanks,
Jason Szrom
Engineer
Solar Energy Systems, LLC
1205 Manhattan Ave
Suite 1210
Brooklyn, NY 11222
718-389
,
Jason Szrom
Engineer
Solar Energy Systems, LLC
718-389-1545 x13
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray
Walters
Sent: Monday, October 26, 2009 6:35 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] NEC 110.13 - Mounting
s for buildings are not typically driven in NYC. Usually the building
steel is bonded to the water main or in some cases a ground conductor ring is
installed under the foundation and bonded to the base of all the building steel
columns.
Regards,
Jason Szrom
Engineer
Solar Energy Systems, LLC
718-389
Howie,
I've looked at a few different MC cable manufacturer data sheets and I can't
find a distinction between AC or DC. In general I wouldn't expect there to be a
difference since AC RMS voltage and current ratings are sort of a 'DC
equivalent'. But the only way to be sure is contact a cable m
Hi William,
I don't have a lot of experience with battery OCPD, but I did have a project
where we used a Square D heavy duty safety switch to protect a negative
grounded 600VDC battery string. All of the heavy duty switches are AC and DC
rated (H363, H364, H365...).
For DC applications, go her
8 matches