[RE-wrenches] PV GEC to the same point as the utility service GEC?

2010-08-19 Thread Jason Szrom
Wrenches, Questions: Does the PV GEC have to be bonded to the ground electrode system at the same point as the utility service equipment GEC? Is there a code section to back this up? Additional info: 1. The DC side of the inverter is a separately derived system and therefore needs a GE

Re: [RE-wrenches] PV GEC to the same point as the utility service GEC?

2010-08-23 Thread Jason Szrom
ilding inspector" Lafferty From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szrom Sent: Thursday, August 19, 2010 7:38 AM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] PV GEC to the

Re: [RE-wrenches] useful info on wire color coding

2010-08-23 Thread Jason Szrom
My 2 cents on this issue which I have encountered on numerous occasions. Here in NYC the majority of service switch installs agree with the convention of BLACK, RED, BLUE. However, I have seen a few older service switches with the reverse, BLUE, RED, BLACK. The only documented place I have ever

[RE-wrenches] NEC 110.13 - Mounting of Combiner

2009-10-26 Thread Jason Szrom
(A) Mounting. Electrical equipment shall be firmly secured to the surface on which it is mounted. Has anyone ever had a problem with this during an inspection? Thanks, Jason Szrom Engineer Solar Energy Systems, LLC 1205 Manhattan Ave Suite 1210 Brooklyn, NY 11222 718-389

Re: [RE-wrenches] NEC 110.13 - Mounting of Combiner

2009-10-27 Thread Jason Szrom
, Jason Szrom Engineer Solar Energy Systems, LLC 718-389-1545 x13 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray Walters Sent: Monday, October 26, 2009 6:35 PM To: RE-wrenches Subject: Re: [RE-wrenches] NEC 110.13 - Mounting

Re: [RE-wrenches] Water Pipes as Grounding Electrodes

2010-01-07 Thread Jason Szrom
s for buildings are not typically driven in NYC. Usually the building steel is bonded to the water main or in some cases a ground conductor ring is installed under the foundation and bonded to the base of all the building steel columns. Regards, Jason Szrom Engineer Solar Energy Systems, LLC 718-389

Re: [RE-wrenches] MC Cable for DC runs

2013-10-21 Thread Jason Szrom
Howie, I've looked at a few different MC cable manufacturer data sheets and I can't find a distinction between AC or DC. In general I wouldn't expect there to be a difference since AC RMS voltage and current ratings are sort of a 'DC equivalent'. But the only way to be sure is contact a cable m

Re: [RE-wrenches] Sunny Island Battery Disconnects

2014-02-10 Thread Jason Szrom
Hi William, I don't have a lot of experience with battery OCPD, but I did have a project where we used a Square D heavy duty safety switch to protect a negative grounded 600VDC battery string. All of the heavy duty switches are AC and DC rated (H363, H364, H365...). For DC applications, go her