[RE-wrenches] String fuse blown

2025-04-11 Thread Amos Post via RE-wrenches
Hi Wrenches, I have a bit of a puzzler that I’m trying to get sorted out. I’ve been servicing a Grid-Tied Battery Backup system that’s about 17-18 years old. The system comprises of 2-GVFX3648s in series, with 2-MX60(at least I think they are 60s) CC’s. Each CC has 3 strings of 3 tied to it,

Re: [RE-wrenches] String fuse blown

2025-04-11 Thread Jay via RE-wrenches
I would do 2 things. 1. If it’s string 3 fuse blowing, swap string 3 to another fuse. 2.  Replace the fuse holder, which is what I suspect is the issue. It’s a weak connection causing heat which is causing the fuse failure. JayOn Apr 11, 2025, at 8:07 AM, Amos Post via RE-wrenches wrote:Hi Wrench

Re: [RE-wrenches] String fuse blown

2025-04-11 Thread Mac Lewis via RE-wrenches
Hello Amos, Have you checked for voltage imbalance for each string? If you have a bad diode, that string may run low on voltage and be trying to send current toward the weak string (this is the reason you have these breakers). I'd run each string independently and see what Vmp is. If you are mi

Re: [RE-wrenches] String fuse blown

2025-04-11 Thread david quattro via RE-wrenches
One time I had similar, but different problem: 1 Amp ground fault fuse consistently blowing, sometimes after 1 day sometimes after weeks/months. I tried everything - replaced home runs, checked VOC, VMP, swapped DC input into a different inverter, etc. it kept coming back to this one string. I che

Re: [RE-wrenches] String fuse blown

2025-04-11 Thread Jerry Shafer via RE-wrenches
Wrenches, Amos, blowing of a 15 amp fuse is not a ghost in the machine, it is an actual issue no way around it, shorted modules, shorted diodes, in most cases it's a home run, way back when USE-2 white wure was failing and would crack and break off mostly this would result in a GFI trip. The fuse i