Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread rick--- via RE-wrenches
Confirmed! Reading the same points on a different inverter yielded the same results. At a different site, I measured -188.8VDC to ground on both L1 and L2. My suspicion is that there’s leakage current via the H-bridge output. Just a thought. Case closed, thanks. Rick BrownSolshine Energy Solar Elec

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread William Miller via RE-wrenches
Rick: You’re OK leaving this random high voltage DC on the AC output? William Miller Miller Solar.com 805-438-5600 www.millersolar.com On Wed, Oct 16, 2024 at 6:09 PM r...@solshineenergy.com < r...@solshineenergy.com> wrote: > Confirmed! Reading the same points on a different inverter yielded

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-16 Thread rick--- via RE-wrenches
Sorry I wasn’t clear. There’s no PV tied directly to the Sol-Ark however the Sunny Boy has 5.52 kW of PV. Again the SB is AC coupled to the Sol-Ark via its Load input/output. I can assure you that the DC is not coming from an external source. There are no faults at either inverter (measured or