We learned of this major deficiency after an eight unit install. No cool
down is disastrous to modern diesels. Our work around was installing a
400amp contactor and macromatic programmable relay.
On Thu, Sep 14, 2023 at 10:05 PM Jerry Shafer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wro
I just replaced two Sunny Islands and one Sunny Boy that I did not install
with a single Sol-Ark 15k today. The generator installer (not me) had
already installed a custom but simple time delay relay. I didn't get into
the logic of it, but from what I understand the generator already had a
cool-dow
In an off-grid scenario I would suggest utilizing the grid connect timer as
a Gen warm up. I typically set this qualification time to 30 or 60 seconds.
Sol Ark fixed the problem with dropping the 2 wire start under full load,
so if this is an issue for you, I would update the firmware.
On Fri, Sep
I saw that setting. I didn't have a chance to look it up today, but I'm
going back to the site tomorrow. I'm going to play with that and try to get
rid of the ancillary equipment that is no longer necessary. Thanks for the
tip.
On Fri, Sep 15, 2023, 5:26 PM Chris Sparadeo
wrote:
> In an off-grid
Chris,
Just so that I understand correctly, are you saying that new firmware
allows for generator cool down?
On Fri, Sep 15, 2023 at 2:33 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I saw that setting. I didn't have a chance to look it up today, but I'm
> go
Jason, Wrenches
I am familiar with Franklin and when I asked them about the battery they
had all the answers but when I asked about the AC coupled inverter inside,
mainly who made it is it field serviceable I got deer in the headlights and
a few weeks later I asked them the same thing and again no
William, Wrenches
Yes I do and it does require some basic electronics to make it work
correctly, you will need to remove the ttemp sender and make a
resistor pack to simulate the 77 degree reading otherwise it will not
charge properly, for the first one I used a breadboard to set the temp for
what
7 matches
Mail list logo