Does anyone know if Franklin supports their AC-coupled battery solution in
a completely off-grid scenario (no grid present)?
I need to install a demonstration system with ~40kWh capacity to run loads
in an outdoor off-grid facility. It needs to be wall mounted, NEMA 3R, and
have 10kW AC output rat
Friends:
I am commissioning an E-vault battery array to an existing SMA Sunny Island
System. Does anyone have any experience with this they could share?
Thanks.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
___
I believe they do. They also have generator support with programable SOC
trigger points. They can start either 2 wire start generators, or if the
generator is existing and has a complicated signaling system, you can actually
wire the Franklin smart module to the existing generator ATS and let F
Enphase does generator support as well. Fortunately, I do not need that, so
maybe it opens up my options. It's good to know that Franklin supports
off-grid. I will reach out to them to confirm.
I asked my Enphase rep to run this up the chain of command to see if they
would support this installatio
Hi All,
I have a client with a sol ark and it doesn’t have warm up or cool down, kind
of amazing companies are going backwards in their tech.
Has anyone come up with external fix for this?
I am guessing the internal relay on the sol ark switches closed when it sees
the correct volts/hz and o
Jay, wrenches
ASCO makes multiple ATS controls that can manage delays latching up and for
cool down. Most of the gensets have are programmed cool down after relay
opens so its not an issue. Generally on start up the genny connects as soon
as it's voltage and freq are within range.