The new solark 15 has a 200 amp rated contactor this is so if you want to
have whole home pass through you can but if you only have an inverter then
use that as your starting point and if the genny is contributing then add
that is, you do not need 2/0 for a single 15 k off grid but you may
I think the idea here is that 690.9 allows the inverter output conductors
to be sized based on the maximum ampacity and an OCPD is actually not
required is the conductor ampacity is sufficient. So in an off-grid
scenario, the wires could be as small as #4. In a grid interconnected
situation where t
Does anyone have a solution for operating a remote trip MN battery breaker
since the BDM is gone?
We do have a birdhouse, so maybe someone has a BDM, but otherwise,
what to do?
Batteries in a dwelling
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorad
I want to comment, maybe without value. The breaker you mention is called
a "shunt trip" breaker. This is common type breaker in the electrical
industry. The MN breaker has a 24 volt solenoid that trips the breaker.
Shunt Trip breakers have the solenoid voltage for the system voltage. BUT
the w
I understand that MidNite is working on a new product to replace the BDM.
Makes sense actually. I don't know any more than that though.
Robin Gudgel would know more.
boB 🌜
boB Gudgel 🌜