Wrenches, I just added a 2nd VFX3648 stacked as SLAVE L1 to increase
charging of his new eVault 18.5 from 12kw Kohler gen. It connects to the
generator but doesn’t charge. I read in the manual that both inverters
must be the same firmware revision. Once hooked up I found that the added
inverter w
John,
I've never faced your situation so can't address it directly. However, I
don't think matching firmware requires replacing a control board. Can't
you just update the firmware to the latest for that legacy product using
a Mate3?
The firware for these should be available at
https://www.outb
Allan,
The new VFXR has updatable firmware through the MATE3 but the old series
has firmware on the control board but not updatable. I have run into this
before but lucked out that both older inverters had the same firmware.
John
On Sun, Mar 20, 2022 at 10:55 AM Sindelar Solar
wrote:
> John
Do you have the proper hub 10.3 installed? And are the jumpers set
correctly? Mate3S? it almost sounds like the slave is set in the Mate not
to charge. And if not plugged into the correct hub port, stuff like this
happens also. And the Mate3 might not work properly with newer inverters,
as I rememb
I just checked my stock of control boards and just happen to have a
new unopened in the box that is firmware #68, same as the new used inverter
I installed. I guess to be sure Outback wont have any other suggestions, I
will install the new board. I charged the customer enough for the used
Is the wiring 120/240 and Series or Parallel stacking? If parallel, one of the
stacking options assumes you have a x-240 transformer and the slave is silent
unless power save is high enough. Pick the parallel that keeps both inverters
on at the same time This is kinda foggy since it has been a
>
> The system is 120v only from the generator and the house is 120 only.
>
John
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserv
John:
I have operated FX inverters of different firmware in one system (not
FXRs). I was told the newest firmware should be in a lower port but the
system worked more reliably with the newer firmware unit in the higher
port. May be worth experimenting. Good luck.
William Miller
On Sun, Mar 20,
HI John,
Yes Its my understanding that they are backwards compatible.
So put the newer inverter as master, older as slave should work.
Jay
> On Mar 20, 2022, at 8:14 AM, John Blittersdorf
> wrote:
>
> Wrenches, I just added a 2nd VFX3648 stacked as SLAVE L1 to increase charging
> of his n
And can't you just wire up the new inverter as a "dumb" battery charger
only? If you don't need to double KW to loads, don't try to stack it, or
connect it to the hub. Just cable it to the batteries, and wire the genny
to it's AC in. NO AC out wiring. When genny is running, it should charge
fine. A
The Sunpumps controller only requires solar panels as DC input. You do not
need a charge controller.
On Tue, Mar 15, 2022 at 12:49 PM William Miller
wrote:
> Windy:
>
> Thanks for the info. I have been in contact with Sun Pumps. They can sell
> me a pump that will work off of a high voltage batt
11 matches
Mail list logo