[RE-wrenches] Fwd: Well Pump Sizing

2019-04-25 Thread Amos Post
I have an off-grid customer who is having problems with his 10 year+ old 1/2hp well pump. It is running and running at 900watts constant and hardly building pressure and even caused the 250amp breaker on his single VFX3524 inverter to trip. He is running the pump at 240V off a x240 transformer an

Re: [RE-wrenches] Fwd: Well Pump Sizing

2019-04-25 Thread Andrew
Hey Amos. It could be a multitude of things depending on what type of pump motor it uses. Even if you get it fixed it’s still got 10yr parts in it elsewhere that will have to probably be replaced soon too. Have you looked into the Grundfos SQF series? They are really nice, run o

Re: [RE-wrenches] SMA Micro-grid

2019-04-25 Thread louis
The Inverters do not know what the wattage will be until they attempt to connect(go into GRID Monitoring routine) and then evaluate the conditions.If the PV voltage is over the Start voltage they will act on this.If by just entering the GRID-Monitoring the PV voltage collapses(not enough minimum po

[RE-wrenches] Tell me what I'm missing on 690.12 B(2)? Where does it say "module-level???"

2019-04-25 Thread Howard Arey
The wording in 690.12 B(2) , effective after Jan 1, 2019, says "The PV System shall comply with one of the following:" In none of the three subsequent paragraphs does it ref to "module level shutdown." Paragraph 2 says gets inside the array voltage under 80 volts within 30 seconds so I understand

[RE-wrenches] Micro inverter OCP

2019-04-25 Thread Jay
Hi all, For micro inverters, what OCP is available for ground fault ( or arc fault) for roof top mounted on a living structure? Thx Jay ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Micro inverter OCP

2019-04-25 Thread Brian Mehalic
Is this in regards to 2014 NEC 705.12(D)(6)? This requirement was deleted in 2017. Brian Mehalic NABCEP Certified Solar PV Installation Professional™ R031508-59 National Electrical Code® CMP-4 Member (520) 204-6639 Solar Energy International http://www.solarenergy.org SEI Professional Services h

Re: [RE-wrenches] Fwd: Well Pump Sizing

2019-04-25 Thread Dave Angelini Offgrid Solar
Time for a radian and lose the x240. Modernize the system to split phase and test for pressure leaks, pressure tank, pressure switch. My experience with the x240 got much better when Schneider, Outback went split phase. They are fine for solar people but one more headache to an offgrid homeowne

Re: [RE-wrenches] Micro inverter OCP

2019-04-25 Thread Nick Soleil
Hi Jay, ArcFault protection is only required for systems operating over 80V, so isn't required for most microinverters. Enphase microinverters include ground-fault protection integral to the microinverters and the GFI can be reset if it trips. Enphase provides instructions on reseting a tri

Re: [RE-wrenches] PV waste problem

2019-04-25 Thread Michael Welch
Hello Wrenches. If you have any questions or concerns, please contact me off-list. This very interesting and important topic can be taken up at length on the RE-Markets email listserver. I'm assuming Eric will be starting the conversation soon, so if you're not already on that listserver, you

Re: [RE-wrenches] Micro inverter OCP

2019-04-25 Thread Will White
Jay, You're triggering some serious PTSD with this question. When 2017 NEC came out Mass was the first state to adopt it and the inspectors started requiring arc fault breakers on the micro inverter branch circuits, we were using Enphase. At the time they didn't work, weren't really listed for bac

Re: [RE-wrenches] Fwd: Well Pump Sizing

2019-04-25 Thread Sindelar Solar
Amos, I have done this and it works. The VFX3524 will run a 3/4 HP (and a 1 HP) AC well pump just fine through a PSX-240. I have this setup in my own home now, running on a 120V Magnum 4024AE. I would suggest a soft-start AC pump with a conventional pressure switch, not the constant-pressure