I've done it twice without a smart phone or tool
kit. Both times, Enphase tech support walked me
though it. The second time it went smoothly. It
takes an ethernet cable from a laptop to the
Envoy. It really is fairly straight forward if it
goes the way it should, which may or may not be the ca
Greetings, Wrenchies~ Sorry to add noise to the List but I messed up
sending the images yesterday.
First attached .png image is from page 2-9 from
Schneider's Conext-XW-Multi-Unit-Power-System-Design-Guide-975-0739-
01-01_Rev-C_ENG.pdf
Additional details would be welcomed from the group, if avail
Hi August,
We have understood that exception to apply only to the DC side. The inverter
output circuit would fall into typical ground sizing requirements which do
state
that the EGC should be upsized proportionally to the other conductors that
are
upsized for a voltage drop.
Cheers,
Dave
*--*
Once again, the '/Definitions/' Geek leers his ugly head. 690.45
specifically applies to /PV Source/ and /PV Output/ /Circuit/s only.
Checking the definitions in 690.2, both are defined as DC and before the
inverter. In your case, the circuit is defined as an /Inverter Output
Circuit/. You
*Scenario*
- 600A *dedicated PV* subpanel w/ (6) 100A circuit breakers, each
feeding a 60kW inverter (72.2A rated output)
- Subpanel is fused at 600A and connects to a larger main
distribution/combiner panel along with other similarly configured subpanels
*Question*
- Must the mai
We have installed several LG Resu10H batteries with Solar Edge StorEdge. One
just happened to be my house.
I have an eGauge system ay my home so I'm seeing what others might not be
and that is an odd "sharks tooth" solar production curve.
These have been bluebird clear solar days in Texas b
Corey,
Here's my interpretation. If anyone can point out where I am in error, I would
appreciate it if you could correct me.
I just quickly reviewed 705.12(D)(2) and it appears that neither of your sizing
calculations are quite right.
Bear in mind that the maximum current of the inverters is d
I have! It was with the RESU10 and not the 10H. It took some time for me
to convince the Engineers i was working with that this was an issue. They
called it micro-cycling and I called it not typical for an offgrid battery
system and possibly wearing the battery for no reason. They did fix it and
I