Good morning! I went to bed wondering if the off-grid battery bank sizing
rules that I use for PV systems hold true for hydro-based systems. I woke
up and I was still mulling this over.
My battery bank sizing standard is to use the method outlined in the SEI
Photovoltaics Manual. I would presum
Hi Matt,
Short answer is yes, 2 days of autonomy should be fine. I am presently
operating our off rid PV/hydro system at well under two days of autonomy.
I just crunched some numbers for our situation here in Vermont. Off grid system
that is now 4.3kW PV and with a Harris micro-hydro turb
Matt:
I have a question for you: I have often considered mounting Class T fuses
directly to a bus bar as you have done. Are you ever worried about physical
strain on the fuse itself without a fuse holder?
Thanks again for all of your input.
William Miller
Lic 773985
millersolar.com
805-438-
Hi Folks,
I was called by a customer with the complaint of the MS4024 inverter shut down
and ME-ARC controller and Trimetric acting strange, intermittent and even even
showing 29 volts at times.
The batteries are four 2.5 year old US battery L16XC 380 AH and checking each
battery showed one at
I am scheduled to be going out to a site in a couple of weeks that is
experiencing frequent shutdowns and I've offered to investigate why the
shutdowns are occurring. The site is 208 3 phase with six Sunny Islands
and Aquion batteries. I've got SMA tech support aware in case I need to
talk with
Hate to be an ass, but look in the mirror! There is NONE! The battery set point
voltage w/ the SMA Aquion BM200 is ~57.5V UNLIKE all the other inverter manu’s
suggestions of 59.8 V. Contact me off list if you want additional thoughts. TUMP
> On Apr 26, 2017, at 12:31 PM, ga...@solarindependence.c
Wallace,
I installed some Interstate RE batteries (green case) L16's that
supposedly are made by US Battery. As with Trojan and other High Capacity
L16's I had several cell failures. I have always felt that gleaning more
amp hours from the same box must lead to cutting corners on robustness.
Here's a thermal image from a recent inspection of 2 v Trojan L16REs.
Notice the normal batteries above and below, they are cool blue, running
around 75F
2 of the cells of the center battery are obviously shorted. Cell
voltage was 2.07 v compared to about 2.3 to 2.4 v for surrounding good
b
Hey everyone,
I'm replacing my old DC 24V shurflo well pump with a new Grundfos 15
SQ05-110. It's the 120V AC model.
Question: The Shurflo required 2 wire cable with no ground, the Grundfos
has black/white/green.
Can anyone think of a good reason why I should replace 100' of expensive
submersible
Maybe I should clarify here that the wire type switches at the well head,
and that is the point at which the metal well casing is bonded to the EGC
running with the current carrying conductors to the supply circuit 20A
breaker.
On Wed, Apr 26, 2017 at 7:09 PM, Rebekah Hren
wrote:
> Hey everyone,
Greetings William,
Good point. This is something I always take into consideration. I
have used Class T Fuses in many situations with and without their fuse
holders. In the case of the installation shown in my custom DC Bus
System pictures the wire/cable type and wire management avoid putting
to