I'm looking for two SMA HF inverters (2, 2.5 or 3 kW), new or used, but
gotta be working properly.
Please contact me off-list.
Thanks,
marco
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Hello Wrenches,
Hope you all had a nice Thanksgiving.
I have an AHJ asking for the service panel buss rating and the service panel
buss protection rating.
Am I correct to assume that the rating is the service panels designated rating
x 1.2% (ie 200A x 1.2 = 240)?
and that the buss protection
As a rull we will only use panel rating 200 is 200 not labeled is in
question
Jerry
On Nov 30, 2014 1:45 PM, "Wayne Irwin" wrote:
> Hello Wrenches,
>
> Hope you all had a nice Thanksgiving.
>
> I have an AHJ asking for the service panel buss rating and the service
> panel buss protection rating.
We're still not at the bottom of it. Seems Mitsubishi is doing their level best to finger the RE system. Yes, the current wave form (On a Fluke 43 Power Analyzer) has a shoulder.. looks down right funky on one inverter thru the X240 until the 2nd inverter lights. Current also looks funkular when ea
Hello Wayne,
Seems to me like the AHJ is asking for the bus bar rating of the main load
center which is usually printed on a sticker inside the panel (only visible
with the dead front removed).
Then he also wants the rating of the main breaker that is installed to protect
the panel (read right o