Re: [RE-wrenches] Magnum inverter remote lightning protection?

2013-04-27 Thread Chris Mason
You can get a telephone line lightning protection device, we install them on PBX incoming lines. Put one on both ends and ground properly. http://www.citel2cp.com/rs485_rs232___industrial_network_surge_protection-g-17-en.html Chris Mason Comet Systems Anguilla (264) 235-5670 St. Kitts (869) 662-

[RE-wrenches] CU 200 error

2013-04-27 Thread frenergy
Wrenches, I have been asked to repair a Grundfos SQ installation for our area Land Trust. Pump is not pumping and the controller (CU200) is throwing a code of: F3. The manual says loose wires, bad connection, failed CU200 or failed pump. I'm looking for more experience than mine in t

Re: [RE-wrenches] CU 200 error

2013-04-27 Thread Roy Butler
Hi Bill, The dreaded F3..with over 40 Grundfos systems out there, I've seen several of these. The most likely cause is a bad connection and the most common of those are the splices underwater. I h

Re: [RE-wrenches] large ground mounts

2013-04-27 Thread Chris Mason
Jay, We installed a 30KW ground mount with SnapNRack ground mount equipment and we were very happy with the strength and ease of assembly. There are some pictures here. https://plus.google.com/photos/100395170796297776118/albums/5758886683698184561 On Sat, Apr 27, 2013 at 12:06 AM, David Katz wr

[RE-wrenches] Wire Gutters

2013-04-27 Thread Aaron Mandelkorn
I often see DC and AC wires contained in the same wire gutters and am wondering what people are doing to comply with the NEC. Doesn't there have to be a physical barrier between AC and DC wires. I like how gutters under multiple inverters and disconnects really clean up the installation but am

Re: [RE-wrenches] Wire Gutters

2013-04-27 Thread August Goers
Most jurisdictions around here allow the AC and DC wires to be bundled/separated by cable ties. Best, August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Aaron Mandelkorn *Sent:* Saturday, April 27, 2013 2:07 PM *To:* RE-

Re: [RE-wrenches] Wire Gutters

2013-04-27 Thread Chris Mason
NEC allows AC and DC in the same raceway as long as they are of the same system. On Sat, Apr 27, 2013 at 5:07 PM, Aaron Mandelkorn wrote: > I often see DC and AC wires contained in the same wire gutters and am > wondering what people are doing to comply with the NEC. Doesn't there have > to be