Is it possible for you to add a 30A contactor with 120Vac coil (which connects
to the grid) to create the ground to neutral bond via the normally closed
contacts?
Thank you,
Maverick
Maverick Brown
BSEET, NABCEP Certified Solar PV Installer ®
President & CEO
Maverick Solar Enterprises, Inc.
O
Hoo boyI've got a tough one here. Trying to troubleshoot an array
ground fault with a system that has 14 strings mounted on a metal roof with
the whole roof and metal framed building being common to ground.
Can anyone recommend any diagnostic tools out there to troubleshoot and
locate grou
Seperate the strings, test the voltage to ground, that will tell you the
faulty string and where the fault is. The voltage to ground divided by the
Voc should tell you how many strings away the fault is.
On Wed, Feb 6, 2013 at 1:57 AM, Marco Mangelsdorf wrote:
> Hoo boyI’ve got a tough one
Marco,
This should be fairly straightforward. If the whole roof is truly grounded,
you have nothing to worry about. If it is not well grounded, then you have
cause for pause.
I would recommend the new Megger MIT410 (or420 or 430) device. It has a 50V
setting which is hugely beneficial for t
Has anyone been in touch with Southwest Windpower lately? We are trying to
order a replacement part. No Luck. We have left numerous messages.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine
They sold everything but Skystream to Primus, very recently.
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy
Rodriguez- All Solar Inc.
Sent: Wednesday, February 06, 2013 9:13 AM
To: re-wrenches@list
And it appears Whisper is now orphaned except for "valid warranty claims."
--
Whisper:Our Whisper turbines will no longer be available for sale, but
Southwest Windpower will continue to support valid warranty claims.
These exciting developments will allow Southwest Windpower to focus our
efforts
Jeremy and All Wind Wrenches,
SWWP is going through some shake-up in the company. People have been laid off.
They have sold off the Air products to Primus Windpower.
http://www.primuswindpower.com/ Contact Ken Kotalik (formerly of SWWP) at
928-607-7034.
They still have the SkyStream but I hear
A month ago I was searching for an Energy Star RF of standard kitchen appeal
for my rental house and with the Wrench groups help I found one I am very
pleased with so far.
Whirpool WRTL9SZY 19 Cubic Foot, Freezer on top no ice maker. $ 800
delivered
Energy Guide Yellow Tag states 345kWh/Yr.
Dear Folks:
Generally with wire runs being short from battery to inverter (in this case SMA
SI) we prefer the largest conductor possible.
Inverters don't like being choked off by wire loss when big loads or
significant charging needs the amps.
2 X 2/0 sounds like a great minimum to me, and yes
Marco,
I second Chris' suggestion. Disconnect all strings at the combiner. Check
VOC PV+ to ground, and PV- to ground on each string, and PV+ to PV-. This
should point you to the faulty string. If the string consists of 10
modules, each with VOC of 30 volts then you should see +300V from PV+ t