[RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread Eric Stikes
Hi Wrenches, I inherited an off-grid PV system that seems to be significantly under producing. I have: 12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated on new 15A breakers in a new Midnite combiner, Output of combiner passes through a 60A breaker then into a SolarBoost 50

Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread jay peltz
Hi Eric, Try putting the SolarBoost 50 into EQ. This will bypass the current limitations and you will see full amps. If no change, then try with 1 string at a time. If still the same then bypass the controller and test with your clamp on. This will tell you if its the array or the SB50 Good

Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread David Katz
I would check each string. I have seen many failed 120 watt Kyocera modules. They had a delamination problem. David Katz Sent from my HTC smartphone on the Now Network from Sprint! - Reply message - From: "Eric Stikes" To: "RE-wrenches" Subject: [RE-wrenches] Troubleshooting Off-grid

Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Eric, Check the dates on the KC-120 module label. If any were manufactured between January 1999 and December 2002, they have or will fail. We have been replacing these modules for over 8 years now. There was a defective solder joint during manufacture. Kyocera will still replace them under w

Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread Roy Rakobitsch
I second what David is saying. I have seen many failed KC120's as well and they seem to fail most often at the top of the module where some insulating tape has been used to isolate the cell interconnecting bus as they pass over one another on their way to the j-box. There will be some slight eviden