Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter outputs

2011-03-30 Thread Jason Szumlanski
Another key is to remember that this discussion also applies to the conductor between the main panel and subpanel. In a large PV system, this could result in a pretty large wire between the two panels, and a significant cost that is often overlooked. In some cases it makes sense to locate the subpa

Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs

2011-03-30 Thread Mark Frye
Jason, I think, going back to the diagram in the article, the feeder breaker is rated at 80A, the feeder conductors are rated at 80A, and the subpanel is rated at 80A, assuming that there are no loads connected in the subpanel. Even if there were up to 100A of loads in the subpanel, you would not

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread Al Frishman
Is a monitoring system installed in the Load Center to measure the cumulative kWh's of the inverter's considered a load? The type of monitoring device I am talking about has CT's that go around the conductors and the Voltage ref is taken by attaching conductors to each phase, the Neutral and the

Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverteroutputs

2011-03-30 Thread Jason Szumlanski
Hmmm. That's not the way I understood it. I could be wrong. 690(B)(2): The sum of the ampere ratings of overcurrent devices in circuits supplying power to a busbar or conductor shall not exceed 120 percent of the rating of the busbar or conductor. In systems with panelboards connected in series

Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs

2011-03-30 Thread Philip Boutelle
To echo the wording in Kent's response, John Wiles has always advised that it doesn't matter if there are currently loads connected to the panel/conductors; if the panel/conductors are capable of having additional loads connected to it, you need to apply 609.64(B)(2). I have had luck with AHJ appro

Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter outputs

2011-03-30 Thread Kent Osterberg
Jason, Now you are opening up a can of worms. It's bad enough that 705.12(D) doesn't say anything about a panel that can't (or shouldn't, or won't) have anything connected but interactive inverters. But when that is the case, a bus rating of 100% of the source circuits should apply. For PV s

Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter outputs

2011-03-30 Thread Mark Frye
Al, I would say that yes the meter is a load and this goes to show the relative inadequacy of the vocabulary we are using in the discussion. In the example we have been using with the 80A breaker, wire and sub panel, you could have up to 80A of loads installed in the sub and still not create an o

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread Kent Osterberg
Al, How about a 15-amp single-pole breaker for power line carrier communications equipment to talk to the inverters? Technically, I think either way they are loads and that changes everything. But in my opinion they are minor and should be allowed without considering the sum of all sources. K

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread David Brearley
This is diagram is based on a 3-phase 208 V service, as clarified in the text accompanying the diagrams. There is a mistake of sorts, however. The authors¹ original manuscript called out a ³generic² 7500W inverter connected to 50A, 2-P breaker. We then added more detail, calling out a Fronius 7500W

[RE-wrenches] NABCEP Stamp

2011-03-30 Thread Troy Harvey
I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have a city agency who is comfortable with the NABCEP certification as a qualification, but would like to see a stamp. Has anyone out there done this? Troy ___ List sponsored by H

Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter outputs

2011-03-30 Thread Brian Teitelbaum
Wouldn't a fault in that conductor between the main and the sub have a potential for up to 160A of current? I would think that at noon on a sunny day, the inverter system could produce 80A from one direction (albeit really only the max amperage outputs of the inverters) and 80A of grid current f

Re: [RE-wrenches] sizing a sub-panel used tocombine multipleinverter outputs

2011-03-30 Thread Mark Frye
That is a really good question Brian. Mostly when thinking about these sizing issues I think about overload conditions and not so much about short-circuit and ground fault conditions. So two questions come up: 1 - What does a UL1741 inverter do when it is connected to a line that is experienc

Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter outputs

2011-03-30 Thread Andrew Truitt
I concur with Jason and Brian's interpretation of 690.64(B)(2). I think one of the intents of the code is to ensure that if there is a fault in a busbar or conductor and the maximum amperage is being delivered to that fault from all OCPDs supplying it (solar + utility), the busbar or conductor sh

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread Jason Szumlanski
Here is a 690.64(B)(2) opinion from Wiles that may help. http://www.fafcosolar.com/download/409/690%2064%28B%29%282%29TECH-1.pdf It's still my contention that the conductors need to be sized for 150A in this example, unless an exception is made by the AHJ. If David Brearley's post about Wiles

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Andrew Truitt
Troy - I have not encountered this before but would you mind sharing what city agency you are refering to? NABCEP is always interested in hearing about these types of "unconventional" uses of the certification. For a brighter energy future, Andrew Truitt Principal Truitt Renewable Energy Consul

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread David Brearley
Agreed: http://solarprofessional.com/article/?file=SP2_3_pg16_QandA_2&search= You¹ll notice that none of the more permissive proposals that John mentions here actually made it into NEC 2011. On 3/30/11 1:07 PM, "Jason Szumlanski" wrote: > Here is a 690.64(B)(2) opinion from Wiles that may hel

Re: [RE-wrenches] sizing a sub-panel used to combinemultiple inverter outputs

2011-03-30 Thread Kristopher Schmid
By this argument, wouldn't it be necessary to check every conductor in the backfeed path adding potential PV amps to their required ampacity including the utility conductor from the transformer? Kris Legacy Solar, LLC 864 Clam Falls Trail Frederic, WI 54837 715-653-4295 sol...@legacysolar.com ww

Re: [RE-wrenches] sizing a sub-panel used tocombinemultiple inverter outputs

2011-03-30 Thread Jason Szumlanski
I hope there are no potential loads between the meter and the transformer, so no! Technically, if it is a supply side tap, the evaluation would include the conductor from the meter to the main distribution panel I believe, but if it is a load side connection it does not matter because of the main b

Re: [RE-wrenches] sizing a sub-panel used tocombine multipleinverter outputs

2011-03-30 Thread Exeltech
Per your question: > 1 - What does a UL1741 inverter do when it is connected > to a line that is experiencing a short-circuit or ground fault? Presuming a hard short, the voltage in that circuit would be essentially zero, and a UL1741 compliant inverter would cease producing power in less than

Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs

2011-03-30 Thread Mark Frye
Right, so going totally on the fly at the white board, let's say we have an inverter with a 45A AC output, it see's the short and pours it's little heart out at 45A for 0.1 sec before shutting out, delivering 4.5 A-sec of energy into the fault. Meanwhile we take out a clearing time curve for the g

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Bob-O Schultze
Troy, On Mar 30, 2011, at 10:04 AM, Troy Harvey wrote: I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have a city agency who is comfortable with the NABCEP certification as a qualification, but would like to see a stamp. Has anyone out there done this? Troy I'm with And

Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs

2011-03-30 Thread Exeltech
You're overlooking an important fact. Grid-tie inverters are current-limited devices.  They lack surge capability. Trip times for various circuit breakers vary depending in part on the overload as a percentage of the breaker's ratings and the circuit breaker temperature (for thermal breakers).

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Erika Weliczko
I hate to mention the evil insurance industry. However, a stamp implies some professional liability insurance to me. There are other professional membership organizations (RESNET) that have developed a tailored professional liability insurance package for its credentialed members with a preferred

Re: [RE-wrenches] Expansion joints

2011-03-30 Thread Erika Weliczko
I recently used a Hubbell Killark product for rigid/IMC and was not happy with how the threads of the coupling engaged in factory conduit threads. Crousehinds XJG-EMT series is intended for EMT. And is described as being used indoors or outdoors. The EMT couplings mostly seem to be compressio

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Bill Brooks
Andrew and Troy, While I can't speak for NABCEP, I would expect that NABCEP should be very opposed to this type of use of their logo. NABCEP does not certify the work that a NABCEP certificant does. They only certify that the installer has met the obligations for certification. There is a HUGE

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Peter Parrish
Back in '06 I got a nifty roll of stickers that I think were meant to be put inverters. But we put so much (doubtless important) signage on our systems, I stopped using them. Maybe they might be used on plans. - Peter Peter T. Parrish, Ph.D.,

[RE-wrenches] Forward re: NABCEP Stamp

2011-03-30 Thread Allan Sindelar
Hi everyone, I think that Bill has summed it up very well. Stamps on plans generally imply the review of a duly recognized engineer. NABCEP Certification is not an equivalency to being a PE. I must say that I am pleased to hear the jurisdiction