Re: [RE-wrenches] 690.32(E) + MC?

2009-12-05 Thread R Ray Walters
I think the issue here is 690.32 deals just with 'fittings and connectors', not the actual wire or cable. I believe you meant to reference 690.31 which says 'all raceway and cable wiring methods included in this codeshall be permitted'. But you still have to comply with 690.31E which says it

Re: [RE-wrenches] 690.31(E) + MC?

2009-12-05 Thread dan
Thanks Ray, you're correct, I meant to refer to 690.31(E). and thanks also for your perspective . dbDan BrownPresidentFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 Original Message Subject: Re: [RE-wrenches] 690.32(E) + MC? Fr

Re: [RE-wrenches] wind load

2009-12-05 Thread Rebecca Lundberg
Hi William, Thanks for responding. We have three long rows of modules, with rails attached every other rafter, every 4'. The inspector's argument is that two attachments for one row might be fine, but that the wind load for the entire array theoretically could be born by one rafter, and therefore

Re: [RE-wrenches] Sandia study - WAS Strings and series of batteries with reverse return linkup

2009-12-05 Thread jay peltz
HI Allan, Here is an interesting way that statistics can make bad results. It might be that 64% of all solar batteries are VRLA, but I would guess that most of the those "systems" are single battery ones. Such as road call boxes, lighting etc which number in the 10's of thousands of systems but

Re: [RE-wrenches] 690.32(E) + MC?

2009-12-05 Thread Dave Click
I believe that in a Code Corner back in the '05 era, John Wiles had said that MC cable was OK to use, then in a later Code Corner he says that it isn't; I thought it was because part of the reason for a metal raceway is physical protection, and EMT/FMC would be sturdier than MC. But then I look

Re: [RE-wrenches] wind load

2009-12-05 Thread Kent Osterberg
Rebecca, With three rows and six lags in every other rafter there is a tremendous force on each of the rafters.  Unirac has excellent information in their installation manual that shows all the engineering info needed for ASCE-7, which is meets the  requirements for most building departments. 

Re: [RE-wrenches] strong module frames

2009-12-05 Thread Jeff Yago
There have been many posts about modules pros and cons, with several had a side mention as to frame construction, but I don't remember anything that specifically addressed the strongest feames.   I have had a few modules in the 200w size range over the years that just seemed flimsy to me compared t

Re: [RE-wrenches] large array conduit runs

2009-12-05 Thread Jeff Yago
We are starting to get much larger grid tie systems above 100 kW and I still remember very clearly that Target melt down related to conduit that shorted out a bundle of string runs between the array and inverters due to improper allowance for expansion and contraction in the long above roof conduit

Re: [RE-wrenches] Sandia study - WAS Strings and series ofbatteries with reverse return linkup

2009-12-05 Thread wind...@wind-sun.com
I have always wondered about that statistic, and figured it had to be something wrong with the survey - that pretty much confirms it. It makes sense, but to add another skew to it: From Jan 2008 until now, we have sold around $1.6 million in batteries. Of those, not a single one was purchased

Re: [RE-wrenches] wind load

2009-12-05 Thread Dave Click
Something that may help with the inspector would be to alternate trusses. If your array spanned ten trusses, which I'll call A-J, and you have three rows of six rails: Rail #1, 3, 5: attach to A, C, E, G, I, J Rail #2, 4, 6: attach to A, B, D, F, H, J It's not helping his concern on the end tr

[RE-wrenches] Inspector interaction

2009-12-05 Thread Dana
Rebecca, We have encountered this a few years back on an inspector issue [ known by most of the early solar manufacturers as that SOB in CO] that he claimed the issue was subject to AHJ [...@#$%^ Having Jurisdiction] . I went over my inspectors head to his supervisor who saw my logic. The insp

Re: [RE-wrenches] Sandia study

2009-12-05 Thread Joel Davidson
Allan, thank you for this important information. Tom Hund, Bob Hammond, and others at the DOE brought scientific discipline to our work, but they lacked the field experience that Wrenches have. John Wiles, Ward Bower, Bill Brooks and others are better grounded in the real-world and make valuab

[RE-wrenches] Antireflective coatings

2009-12-05 Thread Keith Cronin
http://www.ecmag.com/?fa=article&articleID=10827 Do any of you have any comments on the efficacy of these types of products?___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wr

Re: [RE-wrenches] large array conduit runs

2009-12-05 Thread Keith Cronin
Jeff EMT is fine on the roof. Rigid will add weight to the roof, as well as increase your labor costs to install it. My take away from the Target project after reading the report was they did not use the correct fittings. Coupled with long conduit runs and perhaps not using junction boxes and

Re: [RE-wrenches] wind load

2009-12-05 Thread Chris Worcester
One thing we've had to do here is stagger the connections to the rafters from row to row thus each rafter is secured to, not every other one. This is easy enough to do, and just adds one extra standoff or Quick Mount in your case on the staggered row. (we are in a high snow load area and the idea

Re: [RE-wrenches] Strings and series of batteries with reverse return linkup

2009-12-05 Thread Antony Tersol
Assume 3 parallel battery stings, with identical batteries of internal resistance r. Assume identical wire leads of resistance R. Then when the batteries have the same state of charge and their internal resistances are equal, one can solve for the current in each string. I1 = I3 I2 = I1 r / (r+R

Re: [RE-wrenches] large array conduit runs

2009-12-05 Thread Jeff Yago
Sorry for mis-statement as I was not trying to place blame on the designer or installer of the Target failure which I do not have any first hand knowledge.    My point was that regardless of who did what, the conduit did came loose at a fitting, most likely due to expansion and contraction in a lo

Re: [RE-wrenches] Strings and series of batteries with reverse return linkup

2009-12-05 Thread boB Gudgel
Antony Tersol wrote: Assume 3 parallel battery stings, with identical batteries of internal resistance r. Assume identical wire leads of resistance R. Then when the batteries have the same state of charge and their internal resistances are equal, one can solve for the current in each string.

Re: [RE-wrenches] PV wind load

2009-12-05 Thread Patrick Redgate
Call unirac; find a structural engineer who is green in the good sense (not cents); get specs from the truss manufacturer; speak with his boss. Sent from my iPhone On Dec 4, 2009, at 5:55 PM, Rebecca Lundberg > wrote: Solar is somewhat 'new technology' where I live. :-) I have a building i

Re: [RE-wrenches] wind load

2009-12-05 Thread Kirpal Khalsa
Hi Rebecca..when necessary we often locate the truss company thru the builder or the homeowner and have had very good luck with their engineers giving the their stamp to their own trusses as being capable of having a solar array of the requested size installed on that set of trusses. Typica

Re: [RE-wrenches] wind load

2009-12-05 Thread William Miller
Rebecca: I am not a structural engineer, nor would I second guess a structural engineer's findings. The audacity here is that your inspector posture's him/herself as knowing more than a licensed engineer and is imposing unfair demands. Your maximum responsibility ends with an engineer's proj

Re: [RE-wrenches] Antireflective coatings

2009-12-05 Thread Peter Parrish
This comment comes from a physicist, so I may be more critical that the average bear. To begin with, antireflective coatings have been around for a long time. The trick with antireflective coatings is as follows: (1) Even if the material (e.g. low iron glass) absorbs ~1% of the light in

Re: [RE-wrenches] Strings and series of batteries with reverse return linkup

2009-12-05 Thread Darryl Thayer
This also assumes all the identical batteries are at identical temperature, and it one is slightly warmer or can not lose heat as fast, if being charged it will get warmer. the warmer battery will do what? have a lower vltage, have higher current and receive more heat, and get warmer, this is s

Re: [RE-wrenches] large array conduit runs

2009-12-05 Thread Darryl Thayer
Remember target had two fires. one caused by the conduit cutting insulation and the other by the ground current passing through small module ground leads. Had the grounded conductor not been grounded this other fire would not have happened. We need to move to ungrounded systems. Darryl

Re: [RE-wrenches] large array conduit runs

2009-12-05 Thread William Miller
Darryl: You make an important and valid point. This is why I am interested in Aurora Inverters. They use ungrounded PV arrays. Here is a link to the manual. http://www.power-one.com/resources/products/appnote/AlternativeEnergy/manual4.2us.pdf Check out section 2.4.2. Here is the manufactu