Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Eric . Bentsen
Hi Eric, Sounds like a bad control board. Swap the inverter and you should be back in business. Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Repr

Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Steve Higgins
If it's not in search mode, then it sounds like the relay it failing. The SW5548 has two relays, on for grid and one for gen, Does the delay happen using Grid and the Generator? Steve Higgins Technical Services Manager M: +1.206.790.5840 F: +1.902.597.8447 Surrette Battery Company Exclusive man

Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Allan Sindelar
Eric, Ray's suggestion to check the gennie is easy - disconnect the generator's output to the inverter (probably not necessary, but helps to isolate symptoms) and start the generator manually at the gennie. If it shuts down, it's the gennie. Allan