Wrenches -
I wanted to bring up the topic of SMA TL inverters, SPS outlets, and Rapid
Shutdown function. In light of some AHJs where the 2014 NEC is already in
effect, I would appreciate how anyone has insight on how to address the
topics below:
*Re: SPS integrated outlet* - Citing 2014 NEC 690
tly delete the original and any copies of
this email and any attachments thereto. Thank you.
*From:* RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*Mark Byington
*Sent:* Tuesday, October 07, 2014 6:59 AM
*To:* RE-wrenches@lists.re-wrenches.org
<mailto:RE
wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Steve Jefferson
*Sent:* Tuesday, October 07, 2014 8:33 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] TL Inverters
The first gen of TL’s did have a somewhat tight window for the DC window.
However, the new SBTL-US-22 (3kW – 7700kW, wit
..@sma-america.com]
Sent: Thursday, October 09, 2014 11:31 AM
To: ra...@positiveenergysolar.com; RE-wrenches
Subject: RE: [RE-wrenches] TL Inverters & Rapid Shutdown
Morning Wrenches,
SMA is developing a product to meet 690.12 requirements.
It will be shown at SPI in Las Vegas.
Also, you
sday, October 09, 2014 9:41 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] TL Inverters & Rapid Shutdown
Hi Wrenches,
We are being forced to adopt 690.12 Rapid Shutdown requirement based on several
explanations given to our industry:
1. otherwise we would be ignoring the li
e Jefferson
Sent: Tuesday, October 07, 2014 8:33 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL Inverters
The first gen of TL's did have a somewhat tight window for the DC window.
However, the new SBTL-US-22 (3kW - 7700kW, with secure power supply)
Start Voltage is 125, MPPT is
eto.
Thank you.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Mark Byington
Sent: Tuesday, October 07, 2014 6:59 AM
To: RE-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] TL Inverters
Just a word of caution to those not having experience with SMA TL inver
-wrenches.org
Sent: Tuesday, October 07, 2014 6:58 AM
Subject: Re: [RE-wrenches] TL Inverters
Just a word of caution to those not having experience with SMA TL inverters -
the larger units (7-11 kW) have an extremely narrow input DC voltage window.
Depending on your module voltage and string
Just a word of caution to those not having experience with SMA TL inverters
- the larger units (7-11 kW) have an extremely narrow input DC voltage
window. Depending on your module voltage and string design, all you need is
a module or two to be shaded to fall out of the MPPT input voltage range